5 hours ago, Mike Baker said:

Hi Johan, 

the booklet has 2 sets of warning signals that, just to confuse matters, use the same numbers.

An 'error 12' is to do with overheating, a "Fault 12" is leakeage or gfci

An "error 16" is low battery, a "fault 16" is gfci fault. Mine are definately faults as it has a triangle icon with an exclamation point

Most of my settings have been left on default

The system is set up on grid tie with back up 2. I have a 4 x 12v 260 amp sealed lead acid batteries set to charge at:60 A   Floating charge at:54 v   and I don't charge from the grid

Battery specs here: http://www.aasolar.co.nz/AA Champion AGM Deep Cycle Batteries.html  Battery is C12V260  Battery voltage Regulation is 13.6-13.8v

At first I thought the fault was weather related, it still might be for all I know. The system shuts down with a Fault 12 warning mainly in the mornings, and usually if there has been a heavy dew or overnight rain. Once we get to the afternoon it usually runs fine. The other day it was churning out 4.4 Kw and the current was 20amps so it seems to run well.

I restarted the inverter the other night to clear a fault 16 message. There was no PV being generated. I switched off the Solar PV DC isolator switch, the AC Isolator from the grid and the battery isolator. Then reversed the order to switch it back on. Instant fault 12 shutdown, even with no PV.

So I turned it all off and restarted with the PV switch off, it worked fine and I turned the PV switch back on later.

I then switched everything off and tried it without the AC from the grid, as if there was a grid outage. It was running fine until I turned the AC back on and then Fault 12 shut down.

I've included some screen shots of the software settings.

Cheers Mike

 

gridtie.JPG

parameters.JPG

Mike,

You need to consult the battery supplier to ascertain what the absolute minimum cutoff voltage must be for the lifetime you require from your batteries.

The settings which I query are the following:

ac setup of 240v. Google says NZ is 230v

frequency setup as shown. This may be far too wide as it affects the trips. Some overload controls actually use this (and not amps) to monitor overloads.

battery cutoff voltage 40v - divide this by 4 for a single battery and it may be far too low if it really happens. Members may care to comment on this as I have lithium batteries which charge diffently and easily. You need to measure the voltages with a multimeter the next time the inverter reports it as too low to verify what is really happening.

As for the gfci trip - does it mean you have excessive leakage to neutral? You need to eliminate this one by one. I suggest you measure the leakage from neutral to earth to see how much it is. You also make no mention that your gfci trips so it may be faulty. The number one reason in my experience for neutral to earth leakage is a wrongly connected neutral (you need to have a seperate neutral bar for the inverter which is not connected tomthe incomer neutral bar). If everything is connected right it should show zero volts. If you have a clamp meter it will show the neutral leakage in ma which should also be zero (my preferred way).

From the db photos I cannot make out anything. There is a vast difference between the ZA and RSA standards. Is your inverter db seperate from your house db? A wiring diagram will be of more use - this means you will have to trace all the wires between the different components. Without doing this you will be no closer to a solution.

I have just redone my db and it is roughly:

inverter connected to the mains circuit breaker via a 40a overload mcb bypassing the house gfci.

Gfci on the inverter output side connected to a 20a overload mcb with all the low amperage mcbs connected to the gfci.

I still think you need to enable the ac battery charging (but make it late afternoon).

Please post your system performance which shows where all the amps are going to.

Johan

Share this post


Link to post
Share on other sites
1 hour ago, Johandup said:

battery cutoff voltage 40v - divide this by 4 for a single battery and it may be far too low

= 10v which is a flat battery.
Flatter than flat.
Deader than dead.
Below 100% DOD.
Like with a Eskom shutdown
Like in when the rains failed to return 100 days after DayZero (Could not resist.)
... HIGK (Hier Is Groot K..)
 

At that volts, could also be a faulty battery ...

 

 

Dead.jpg

Share this post


Link to post
Share on other sites

Hi Guys,

than you for the input.

The 40v you're referring to is not enabled. I believe it is under the grid charging option. I have never changed the value as I only use PV to charge the batteries.

The error 16 was actually for a low battery, not GFCI fault as I thought.

I'm waiting to hear back from my battery manufacturers re settings.

Cheers Mike

Share this post


Link to post
Share on other sites
8 hours ago, Mike Baker said:

Hi Johan, 

the booklet has 2 sets of warning signals that, just to confuse matters, use the same numbers.

An 'error 12' is to do with overheating, a "Fault 12" is leakeage or gfci

An "error 16" is low battery, a "fault 16" is gfci fault. Mine are definately faults as it has a triangle icon with an exclamation point

Most of my settings have been left on default

The system is set up on grid tie with back up 2. I have a 4 x 12v 260 amp sealed lead acid batteries set to charge at:60 A   Floating charge at:54 v   and I don't charge from the grid

Battery specs here: http://www.aasolar.co.nz/AA Champion AGM Deep Cycle Batteries.html  Battery is C12V260  Battery voltage Regulation is 13.6-13.8v

At first I thought the fault was weather related, it still might be for all I know. The system shuts down with a Fault 12 warning mainly in the mornings, and usually if there has been a heavy dew or overnight rain. Once we get to the afternoon it usually runs fine. The other day it was churning out 4.4 Kw and the current was 20amps so it seems to run well.

I restarted the inverter the other night to clear a fault 16 message. There was no PV being generated. I switched off the Solar PV DC isolator switch, the AC Isolator from the grid and the battery isolator. Then reversed the order to switch it back on. Instant fault 12 shutdown, even with no PV.

So I turned it all off and restarted with the PV switch off, it worked fine and I turned the PV switch back on later.

I then switched everything off and tried it without the AC from the grid, as if there was a grid outage. It was running fine until I turned the AC back on and then Fault 12 shut down.

I've included some screen shots of the software settings.

Cheers Mike

 

gridtie.JPG

parameters.JPG

Mike, 

Your settings was to cut out at 42v for the pv side. As per the above settings it means it passed 100% dod.

A deep cycle battery is not a solar battery. My experience with them doing camping is they have a very short life time and they must not be discharged below 20% dod.

My 8.8kw Pylontech batteries cost 3x as much as my inverter and I could choose between having 4 of them or two batteries plus solar panels for their prize. They are managed by a built in bms which manages everything from safeties, temps, voltages, charging etc. As far as I am concerned it is a set and forget about it system.

Many contributors on the forum reckon this is the way to go as you must compare a 1000+ a bit life cycle solar battery to a 6000 life cycle lithium battery.

A deep cycle might give you 250 cycles - open for discussion on this.

Johan

Share this post


Link to post
Share on other sites
6 hours ago, Johandup said:

A deep cycle might give you 250 cycles

+-250 cycles on 50% DOD.

If lightly used, maybe 5 years and they are done.

Comparing apples with kinda apples, Trojan T105RE's deep cycle solar and forklift approved batteries can give you 1600 cycles at 50% DOD and 4000 cycles at 20% DOD, without breaking the bank too badly when compared to 12v leisure so-called "deep cycle" batteries.

Share this post


Link to post
Share on other sites

Hello, how are the inverters going to those who changed the hardware and firmware ?. The truth is I do not know if I chose the inverter well, the one that stays alive sounds like an old car. I do not have high hopes that they will be fine. Greetings.

Share this post


Link to post
Share on other sites
On 2/7/2018 at 4:15 PM, The Terrible Triplett said:

1600 cycles at 50% DOD and 4000 cycles at 20% DOD, without breaking the bank too badly

I think this is where the Pylontechs are coming in. We're at the point where a good set of Trojans cost the same as a comparable (mostly) Pylontech rack.