gabriel
cable size 48v system, 4x250ah batteries, 4m
hi guys
what would be the right cable size between the batteries [250ah] and the inverter for a 48v system where the total cable length in less than 4m :huh:
Share this post
Link to post
Depends on the maximum current draw of the inverter... the one thing you didn't specify :-)
Let's say it is 5kva. That's about 100 amps give or take. You want a voltage drop of less than 3%, preferably around 1%.
35mm^2 has a resistance of 0.65Ω per kilometer. You have 0.004 kilometer. So
0.004 * 0.65 * 100 ~= 0.3V. That's less than 1%.
25mm^2 has a resistance of 0.9Ω per km.
0.004 * 0.9 * 100 ~= 0.4V. That's also less than 1%.
If you look at some wiring ampacity tables (google) you'll see that the 25mm^2 will run quite hot at full load. So 25 in open air is fine if you only run full load for short periods. I'd go with 35.
Share this post
Link to post
Create an account
Register a new account
Sign in
Sign In Now