isetech Posted November 15, 2021 Posted November 15, 2021 Did my home and I think it is right ... thought I would share to see if I got it right. I want to install and inverter only ... no solar (online type ... maybe a mecer king would be a good selection) The inverter will be used as a backup system for an office. The installation: AC mains 230 VAC 18 amps (a constant 18 amps load ...measured) 4140 watts backup time required ... about 3 hours. DC section: 4140 / 0.7 = 5914.28/ 1000 5.9 KVA (an 8 kva would be required) 0.7 used for inverter losses. 48 VDC 86.25 amps for a 3 hr backup rounded to 90 amps x 3 = 270 Amp/hr The customer will be supplying the batteries and he want s lead acid ... so we need to divide the amp/hr 0.5 270/.5 = 540 Amp/hr If we were looking at lithium then it would just be the amp/hr x VDC 270x48= 12960 w/hr divided by 1000 = 12.96 kw/hr battery. Selection: 1 x 8 kva mecer king in inverter 3 x 5,5kw/hr batteries I also considered a 3 phase inverter ... but decided to stick with the single phase to keep it simple. Quote