Morning

I have a 5kva grid-tie inverter connected to the main grid and also connected to a Selectronic sp pro smart bi-directional inverter/charger. This unit is connected to a 600ah battery bank and feed a separated mains distribution board. I want to expand my system by adding another 3kva grid-tie inverter on the AC side of the bi-directional inverter/charger with 3kva of solar panels and a power diverted to protect my battery system.

Both 5kva and 3kva grid-tie inverters should be able to feedback to the grid when my load is less. When grid falls, the 5kva grid-tie inverter should go down to protect the grid but the 3kva grid-tie should stay up to assist the bi-directional inverter to provide load and to charge batteries.

Will this work ?  - Please advice

 

 

 

 

Posted

I took a change and connected a grid-tie inverter on the AC side with 5 x 300w panels. Everything looks fine and when a drop the grid, the one inverter do go down and the inverter on then AC side says on. Did a load test and was able to pull more than 5kva from the inverter/charger which I could not do before. So it seems the second grid-tie inverter contribute his kw to the 5kw. Did see I will need a power diverter because it do overcharge my battery's when they are full and load are low.

Where can I source a power diverter or better -  something that can put of the inverter when battery's are full and put on the inverter when battery's are on 80% ?

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...