Pylontech UP5000 Axpert(Mecer 5kva) Microwave battery trip


Recommended Posts

Posted

Hi All

Looking for some advice.

I have one UP5000 battery with the Axpert 5kva inverter. When we recently try to start the Microwave the battery tripped and obviously i was not at home when this happened. Anyone have an idea why this happened?>

Posted

I'm guessing that the BMS shut the battery down because it detected an overload. It probably wasn't JUST the microwave. You would have had other loads that added up to close to the Pylontech's maximum continuous discharge of 2400 W or 5 minute burst of 3600 W, and the microwave pushed the total load into overload territory.