elihelou Posted May 18, 2022 Posted May 18, 2022 (edited) Hi everyone, I would really appreciate it if someone can provide me with the following: Latest firmware for SPF 5000 ES Latest firmware for the MPPT Latest firmware for the data logger Latest version of the ISP Tool Documentation for the above I would also like to know your opinion about the current setup and its configuration that I have although I have confidence in the person who installed but I would like to double check if the settings are good enough to keep my batteries efficient and durable. The setup is as per the following them as per the following: 2x SPF 5000 ES running in parallel (firmware: one inverter is 040/041-05-701 and the other 040/041-06-104) 10x Longi LR5-72HPH-545M (each 5 panels to an inverter) 12x Lento lead acid LSTB-22000 (12V 200Ah) - installed each 4 in series (48V 200Ah) and then the 3 series in parallel resulting in a setup of 48V 600Ah -> 28.8 Kwh The whole system is also connected to the utility as well. My inverter settings are as per the following: Program Description Value 1 OPPR SOL 2 CHGI 70 3 ACV APL 4 SAVE DIS 5 BATT USE 6 LDRS DIS 7 TMRS DIS 8 OUTV 230 9 OUTF 50 10 BATN 4 11 ACI 30 12 B2AC 46 13 AC2B 54 14 CGPR SNU 15 BUZZ ON 16 LCDB ON 17 ALAM ON 18 BYP DIS 19 CV 56.8 20 FLTV 51 21 CUTV 45 23 PRLL PAL 28 ADDR 1 37 YEAR 2022 38 MON 5 39 DAY 18 40 HOUR 10 41 MIN 0 42 SEC 0 43 EQ DIS 44 EQV 58.4 45 EQT 60 46 EQTO 120 47 EQI 30 48 EQ OFF 49 CHG TIM 1200 50 OUP TIME 0000 Edited May 18, 2022 by elihelou Quote
zsde Posted May 18, 2022 Posted May 18, 2022 Your cutoff voltage is on the low side, unless you don't mind risking a reduced lifetime of the batteries. Here is a table for typical 12V Lead-Acid chemistry. Multiply those by 4 and decide if you wish to remain in the green band. That would be the suggested cutoff V. Have a look at this thread. All your other questions are answered in there, including the downloads and files you are looking for. https://diysolarforum.com/threads/growatt-spf-5000es-firmware-update.35171/ elihelou 1 Quote
elihelou Posted May 18, 2022 Author Posted May 18, 2022 2 hours ago, zsde said: Your cutoff voltage is on the low side, unless you don't mind risking a reduced lifetime of the batteries. Here is a table for typical 12V Lead-Acid chemistry. Multiply those by 4 and decide if you wish to remain in the green band. That would be the suggested cutoff V. Have a look at this thread. All your other questions are answered in there, including the downloads and files you are looking for. https://diysolarforum.com/threads/growatt-spf-5000es-firmware-update.35171/ Thank you so much for your help. Can you please also check setting 2-12-13-18-19? Quote
zsde Posted May 18, 2022 Posted May 18, 2022 (edited) 26 minutes ago, elihelou said: Thank you so much for your help. Can you please also check setting 2-12-13-18-19? 2 I would leave as is seeing that you are running 12 Batteries 12 I would recommend 48V to ensure the Batteries start charging once they reach 12V 13 - 18 - 19 Leave as is One question. Why are you using "USE" Battery type instead of "FLd" ? Edited May 18, 2022 by zsde Quote
elihelou Posted May 18, 2022 Author Posted May 18, 2022 (edited) 20 minutes ago, zsde said: 2 I would leave as is seeing that you are running 12 Batteries 12 I would recommend 48V to ensure the Batteries start charging once they reach 12V 13 - 18 - 19 Leave as is One question. Why are you using "USE" Battery type instead of "FLd" ? Oh, by the way, i ddnt mean setting 18. Instead, what do you think about #20? I didn't setup my devices, the installer did. I'm not sure why he is using USE instead of Fld. But in any case, if I use Fld, what would be the default settings in this case? do I rely on the default values or do i also need to change them? Edited May 18, 2022 by elihelou Quote
zsde Posted May 18, 2022 Posted May 18, 2022 (edited) 2 hours ago, elihelou said: Oh, by the way, i ddnt mean setting 18. Instead, what do you think about #20? I didn't setup my devices, the installer did. I'm not sure why he is using USE instead of Fld. But in any case, if I use Fld, what would be the default settings in this case? do I rely on the default values or do i also need to change them? Default Fld would preset the typical Leadacid Battery settings. You would still be able to adjust some of them but some may be fixed. USE mode allows you to set everything manually. Perhaps your installer had a look at your specific battery data and decided to rather set everything manually. You basically know what your settings are now, so no harm in setting it to flooded and then you can cycle through the program codes and compare what the default settings are. 20 should be whatever is shown on your batteries as being the recommended float voltages. Normally something like 13,5 to 13,9V (obviously needs to be multiplied by 4). It differs by manufacturer but it is normally printed on every Flooded or AGM Battery. 54V or slightly lower would be my recommendation. Edited May 18, 2022 by zsde Quote
Pjs100 Posted May 19, 2022 Posted May 19, 2022 On 2022/05/18 at 10:55 AM, zsde said: Your cutoff voltage is on the low side, unless you don't mind risking a reduced lifetime of the batteries. Here is a table for typical 12V Lead-Acid chemistry. Multiply those by 4 and decide if you wish to remain in the green band. That would be the suggested cutoff V. Have a look at this thread. All your other questions are answered in there, including the downloads and files you are looking for. https://diysolarforum.com/threads/growatt-spf-5000es-firmware-update.35171/ Would the updated files be ok in South Africa? Or aren't these inverters region bound? Quote
zsde Posted May 19, 2022 Posted May 19, 2022 1 hour ago, Pjs100 said: Would the updated files be ok in South Africa? Or aren't these inverters region bound? As far as I can tell, no, they are not region bound. I was sent the .05 files directly from the International Rep in China. Never updated my inverter to .06 as it is working just fine for me. Quote
TJ Human Posted May 27, 2022 Posted May 27, 2022 On 2022/05/19 at 4:22 PM, zsde said: As far as I can tell, no, they are not region bound. I was sent the .05 files directly from the International Rep in China. Never updated my inverter to .06 as it is working just fine for me. zsde can you send the new firmware to me please? Onmy growatt everything works fine untill I suddenly start pulling a big load from pv, then the inverter cuts off the solar completely even though there should be enough power to pull the loads. Quote
zsde Posted May 27, 2022 Posted May 27, 2022 1 hour ago, TJ Human said: zsde can you send the new firmware to me please? Onmy growatt everything works fine untill I suddenly start pulling a big load from pv, then the inverter cuts off the solar completely even though there should be enough power to pull the loads. Sent you a PM Quote
Paul burgess Posted October 10, 2022 Posted October 10, 2022 I’ve got a forklift truck lead acid battery 58v 468 amps but can’t seem to set up the controller growatt 5000 es to understand my battery can anyone help Quote
DeeDee Posted October 31, 2022 Posted October 31, 2022 For that Battery you should be able to use the "FLD" setting, I think you can only change battery types if the inverter is in standby mode ( switched off at the bottom rocker switch) how do you mean " understand" your battery ? in terms of "state of Charge" these inverters only sense the battery voltage and do a best guess from there, a Victron BMV 712 or similar energy meter should give you a much better idea of battery capacity and state of charge. sidenote : Where does one find these forklift batteries, or locomotive single lead acid cells for a decent price ? Quote