Posted January 8, 20232 yr Hello anyone familar with these menu sertings on an MPS-5500H (they are not even on the original manual) Setting 30: ALL/ONE No idea on this one Setting 31: Pds/ Pen ( i think this one is for PV Max power input = Batt charging power + load power , Enabled. but what what would it mean if it's disabled??) Anyone knows?
January 9, 20232 yr 23 hours ago, mafiose13 said: Setting 30: ALL/ONE That sounds like the PV OK condition; if so, it's silly. Just leave it at default. it only applies when you have paralleled inverters with more than one connected to PV. 23 hours ago, mafiose13 said: Setting 31: Pds/ Pen ( i think this one is for PV Max power input = Batt charging power + load power , Enabled. but what what would it mean if it's disabled??) That sounds like Solar Balance on Axperts. Leave it enabled. If disabled, it doesn't consider loads when figuring out how much PV power to push towards the battery. I can't imaging anyone wanting to use this, unless the calculation was so buggy that you're better off without it. I've not found the calculation to be buggy, or at least not suspected it.