Greenrich Up5000 and Growatt 5000TL-HVM in parallel


ara

Recommended Posts

I'm struggling to get the batteries to work properly with the inverters on Li protocol 02. The Li sign is on, both inverters are connected and the setting 28 (address) is 1 and the other is 2. The inverters are reading the SOC perfectly. I'm using the Rs485 to communicate. 

The problem comes to charging. If you go to setting 2 it shows the whole time 4A and the batteries are only charging at around 220watt.

Any ideas?

Edited by ara
Link to comment
Share on other sites

If you are using Li Protocol, then the BMS populates certain Inverter settings and setting 2 is one of them.
If that is auto populated to 4A, then I suspect corruption in the comms, either incorrect protocol or possibly incorrect dip switch settings.
Were you provided with the Growatt Protocol regimen by the Battery manufacturer?
 

Link to comment
Share on other sites

Did you make up a cable or are you using a "one to one" standard LAN cable?
If you are using a standard LAN cable then you should be using the BMS CAN option which would be the preferred option, i.e. the Protocol 52. Your LAN cable should be in the BMS port on the Inverter.
 

Edited by zsde
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...