Posted March 24, 20232 yr Need some assistance please. Not sure if I have a faulty inverter or incorrect settings. My setup: 1x Kodak Off Grid 5.48 Inverter 1x Pylontech US3000 Lithium Battery Since about a week ago, my inverter failed to kick in during loadshedding. When drawing power from the mains, the inverter shows the battery is charging, and input and output is the same. The problem is when loadshedding occurs (off mains), inverter displays error 04, with the battery icon flashing. Input = 0v and Output = 230v Had the battery tested, and thats working fine
March 24, 20232 yr 56 minutes ago, MisterA said: inverter displays error 04, with the battery icon flashing. Input = 0v and Output = 230v Is it error code F04 or warning code 04⚠? With output voltage showing 230 V and no utility, you should be able to run loads. Oh, unless it's during the day, when perhaps solar power could be providing the 230 V output. But even then, you should be able to run small loads. I'm not understanding "no output" if the output voltage is 230 V.
August 6, 20231 yr Hi, I have a kodak 6.2kw inverter with four pylon batteries. The inverter worked well for a year but now the inverter shuts off the output during the day. It happens randomly and everything on the inverter shows normal.
August 7, 20231 yr 20 hours ago, Molla said: The inverter worked well for a year but now the inverter shuts off the output during the day. What is the battery voltage shown on the inverter when that happens? Is the battery basically full by then? Does the battery show any warnings or errors?