My Electrician has wired my DB board as shown in the simplified schematic below.  I note the following:

  1. The grid-feed to the change-over is taken from the output side of Beaker-A.  If there's a need to make the Inverter DB safe, this would need Breaker-A to be off (and the Inverter) which means there is no supply to essential loads during this time.  Shouldn't the grid-feed to the change-over be tied in before Breaker-A?
  2. For the return to the Main DB there is an MCB on the inverter side (#D), then another in the Main DB (#B), and then the change-over.  Is this all necessary?  The cabling is protected by Breaker-D and the change-over is an isolator.  Taking out Breaker-B opens up two DIN rail slots which would help me.

Any thoughts?

Thanks

image.png.41779bf6dcf6d3e98f197c546c1aad2b.png

Link to comment
Share on other sites

30 minutes ago, KeithR said:

Hi all,

My Electrician has wired my DB board as shown in the simplified schematic below.  I note the following:

  1. The grid-feed to the change-over is taken from the output side of Beaker-A.  If there's a need to make the Inverter DB safe, this would need Breaker-A to be off (and the Inverter) which means there is no supply to essential loads during this time.  Shouldn't the grid-feed to the change-over be tied in before Breaker-A?
  2. For the return to the Main DB there is an MCB on the inverter side (#D), then another in the Main DB (#B), and then the change-over.  Is this all necessary?  The cabling is protected by Breaker-D and the change-over is an isolator.  Taking out Breaker-B opens up two DIN rail slots which would help me.

Any thoughts?

Thanks

image.png.41779bf6dcf6d3e98f197c546c1aad2b.png

I am in line with your reasoning on both counts.  But we need to assume that wire/cable thickness as depicted in your drawing are all the same. 

1  technically  feeding the grid bypass from the output of A serves no purpose and its confusing because A is labelled INVERTER. Breaker A serves the purpose of protecting and isolating the inverter grid feed  as it leaves the main box. 

Breaker C  is only there to switch off the inverter in reaching distance from the inverter. Ideally this is an isolator, need not be a circuit breaker. 

2 Breaker D is important as you pointed out and must be a circuit breaker to protect the load cable back to the main box. 

Breaker B  technically serves no purpose at all. 

Other opinions of course are welcome and important. 

 

Edited by BritishRacingGreen
Link to comment
Share on other sites

31 minutes ago, BritishRacingGreen said:

I am in line with your reasoning on both counts.  But we need to assume that wire/cable thickness as depicted in your drawing are all the same. 

1  technically  feeding the grid bypass from the output of A serves no purpose and its confusing because A is labelled INVERTER. Breaker A serves the purpose of protecting and isolating the inverter grid feed  as it leaves the main box. 

Breaker C  is only there to switch off the inverter in reaching distance from the inverter. Ideally this is an isolator, need not be a circuit breaker. 

2 Breaker D is important as you pointed out and must be a circuit breaker to protect the load cable back to the main box. 

Breaker B  technically serves no purpose at all. 

Other opinions of course are welcome and important. 

 

There might be an argument that Breaker B is a convenient point to switch off the incoming inverter output to rest of the main db. I am not 100% sure that this is a COC requirement though. 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...