9 minutes ago, plonkster said:

Not necessarily. Many of these inverters can pass more current than they can generate themselves, for example the 3KVA Multiplus I mentioned can deliver a whole 50 amps on the output as long as the grid is available on the input. As I recall, the Infini also has this feature.

Wow! Ok... This is interesting stuff, so I only need to use the relay to tell me to run to the DB and switch off the Heatpumps etc.

Link to comment
Share on other sites

6 hours ago, KASman said:

Anybody had any experience with Artsolar panels. Prices seem very good

No, but I cant see any reason why their panels would be any better/worse than any of the multitude of Chinese multi-crystalline panels available. I previously used Setsolar panels which are also RSA made and was very happy with the product. Setsolar/Artsolar sound very similar, I wonder if it is not some kind of breakaway?

They are well priced, I would be happy to use them.

Link to comment
Share on other sites

13 hours ago, KASman said:

Wow! Ok... This is interesting stuff, so I only need to use the relay to tell me to run to the DB and switch off the Heatpumps etc.

Some people (see SolarNoob above) use a contactor that is powered by the grid to switch the high load items off when the grid goes out. So these items are connected to the inverter output (so they benefit from the PV), but don't draw it down when there is an outage.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...