Anarchy05 Posted April 21, 2018 Share Posted April 21, 2018 Hi Guys, Could you please assist me in helping a friend, he has an off grid system,on a remote farm. He has a Synerji 5kva,with 9 300w panels,3 in series,connected to 3 in parallel. The inverter is then connected to 8 205ah batteries,also HA-02 per 4 batteries. The issue is that the batteries don't fully charge in one day. And he has to get up at 2-3 in the mornings to start the generator. The loads he has are a box deep freezer and a TV in the house. The lights all run from a 12v system that is separate. I don't know what else to do for him anymore to try and assist Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted April 21, 2018 Share Posted April 21, 2018 Sjoe big ask without any data. I found the Synerji to be a poor clone of the Axpert. According to your information the batteries should EASILY carry the load. The panels should also easily charge the batteries in one day (a sunny one of course). Give us some battery voltages and production figures from the panels and photographs. Quote Link to comment Share on other sites More sharing options...
pilotfish Posted April 21, 2018 Share Posted April 21, 2018 Hi @Anarchy05, The Synerji appears to be a re-branded Axpert, so I believe that you can read all the topics and follow the advice related to the Axpert. It comes in both PWM and MPPT versions, it would be important to know which one he has as the advice may differ in certain aspects. I am going to assume that he has a rebranded version of the AXPERT MKS 5K (MPPT version) with max PV array open circuit voltage of 145Vdc, because the PWM max PV array open circuit voltage is 105Vdc and I think you are exceeding that but some margin already. A 300W panel is "normally" 72 modules, which "normally" has an OCV of around 46Vdc which would mean a current OCV of around 138V for 3 panels in series. This is getting very close to the max allowed for the MPPT and may exceed it in bright and cold winter conditions. 2 hours ago, Anarchy05 said: The issue is that the batteries don't fully charge in one day. My 1st and most obvious suggestion would be more panel. The Axpert MKS 5k (which I believe your inverter to be but I may be wrong in which case all my advice may be nonsense!) can handle 12x300W panels. Most people on the forum would recommend that to be configured 2S6P, but considering yours are already configured 3S3P you could go to 3S4P if not keen on the major panel rewire. Note that 2S6P and 3S4P will give the same amount of power, it is only that the 1st option would give greater safety margin in relation to Max OCV, which I am assuming to be 145V. My 2nd suggestion would be to confirm the condition of the batteries. This can be quite tricky to do while in operation but the following should give a reasonable indication of any dodgy batteries; Remove the HA-02's for the duration of this test as they will confuse the results (but re-install afterwards because they are a valuable addition to your type of battery bank), Run the system as usual for a couple of days without the HA's, On the 3rd morning when batteries are low and BEFORE starting the generator, measure and record the voltage of each individual battery, The batteries should all be at a similar voltage, any that are very low in relation to the others should be considered suspect and more than likely damaged. My 3rd suggestion is to confirm that it is actually an Axpert and exactly which model (check out the firmware version which will give a clue), if confirmed to be rebranded Axpert then reflash with @Coulomb and @weber revised firmware which addresses a charging anomaly in Axpert firmware which causes the system to go to float mode much too early. This will cause battery charge current to drop off too soon so that the batteries are unable to fully charge even when panel capacity is available. Finally I suggest a decent monitoring system such as ICC software from @Manie, because running an off-grid PV system while blind is a very difficult thing to do. If you do go ahead with the ICC software then also add a Victron BMV-702 which will pass proper battery state of charge info to the software and not the useless info delivered by the Axpert. Good luck. Quote Link to comment Share on other sites More sharing options...
Anarchy05 Posted April 21, 2018 Author Share Posted April 21, 2018 I will only be able to give battery voltages when on the farm which is a good 300+km from me. I will get a bit more info about the inverter and come back to you. Thanks for the speedy info. Where can I look for the firmware? Is that in the downloads section? Quote Link to comment Share on other sites More sharing options...
pilotfish Posted April 21, 2018 Share Posted April 21, 2018 4 minutes ago, Anarchy05 said: Where can I look for the firmware? Is that in the downloads section? http://forums.aeva.asn.au/viewtopic.php?f=31&t=4332 Coulomb - Patch Instructions.docx Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted April 21, 2018 Share Posted April 21, 2018 The Synerji I had in my hands had a different firmware to Axpert. It is an Axpert clone rather than a rebranded Axpert. pilotfish 1 Quote Link to comment Share on other sites More sharing options...
pilotfish Posted April 21, 2018 Share Posted April 21, 2018 In which case the reflash may brick the inverter and I dont know if ICC will be able to interact with your inverter - you could use the free version for a week or so if I am not mistaken to evaluate. Quote Link to comment Share on other sites More sharing options...
Anarchy05 Posted April 21, 2018 Author Share Posted April 21, 2018 Yes. I have just reflashed my own inverter after reading about the bug. But I would be hesitant to flash his inverter as the fw might be incompatible. Even the setup with the buttons are different. I am going to ask him to go through the settings on his inverter until I can go look at it. But might recommend him getting a victron mppt rather Quote Link to comment Share on other sites More sharing options...
pilotfish Posted April 21, 2018 Share Posted April 21, 2018 I noted in @Chris Hobson video that the Low Volt shut down seems to be set at 36v (9v per 12V battery). If that is the default then at that setting the batteries would be TOAST! Quote Link to comment Share on other sites More sharing options...
Chris Hobson Posted April 21, 2018 Share Posted April 21, 2018 Default Quote Link to comment Share on other sites More sharing options...
Leonardenzo Posted November 28, 2019 Share Posted November 28, 2019 Error code 77? Quote Link to comment Share on other sites More sharing options...
Coulomb Posted November 28, 2019 Share Posted November 28, 2019 3 hours ago, Leonardenzo said: Error code 77? It doesn't seem to be a standard Axpert error code (Synerjis are not quite Axperts though). It might be one of the new, special codes for Pylontech battery BMS communications; I haven't figured out how to find those as yet. There was a table of such codes (from poor memory), and I can't find it now; I thought it was on this forum somewhere. Sorry I'm not much help. Quote Link to comment Share on other sites More sharing options...
Vissie Posted July 15, 2020 Share Posted July 15, 2020 Morning Has anyone got a user manual on this Synerji 5kVA/5kW 48v Hybrid Plus Inv 80A MPPT What is error 80? Regards Vissie Quote Link to comment Share on other sites More sharing options...
Coulomb Posted July 16, 2020 Share Posted July 16, 2020 22 hours ago, Vissie said: Has anyone got a user manual on this Synerji 5kVA/5kW 48v Hybrid Plus Inv 80A MPPT What is error 80? I don't know. But on an Axpert, this would be "CAN data loss". Is yours paralleled? If not, is the equivalent of AC output mode setting (only available when inverter is switched off, in Axperts) set to "single"? Quote Link to comment Share on other sites More sharing options...
Thapelo Posted August 9, 2020 Share Posted August 9, 2020 Hi everyone. My name ie Thapelo and I am very very new to this topic. I have just purchased a synerji inverter and after installation, it shows error 73. How di I resolve this? Quote Link to comment Share on other sites More sharing options...
Darryl2021 Posted February 12, 2021 Share Posted February 12, 2021 Hi, We have had numerous issues with these inverters. At a stage we had over 15 sitting in the garage with faults in less than 3 months. At a large cost to us we ended up installing Mecer and Kodak units. Must say that Kodak has not yielded us one return (touch wood). If you can afford it, buy once and get a victron system!! These hybrids end up costing money within a few years for those who are lucky to get a few out of them! Quote Link to comment Share on other sites More sharing options...
Irocmaster Posted August 25, 2021 Share Posted August 25, 2021 Hi I hope this help Error code 77 Parameter error Error code 73 Solar charger stops due to high PV voltage No idea what Parameter error mean. Quote Link to comment Share on other sites More sharing options...
Joséhartz Posted November 13, 2022 Share Posted November 13, 2022 My inverter keeps on screaming and when I reset it, all the loghts flashes and still keeps on screaming with all the lights flashing. What can I do? please help. HYBRID SOLAR INVERTER MODEL SYSV18-5K MPK Quote Link to comment Share on other sites More sharing options...
Coulomb Posted November 13, 2022 Share Posted November 13, 2022 8 hours ago, Joséhartz said: MODEL SYSV18-5K MPK That appears to be a clone of an Axpert KS 5K-48. Sorry, I have no answer to your question; it sounds like a drastic hardware failure to me. Fortunately, there are traced schematics for similar models. So if you're handy with electronics, check the AEVA PIP inverter repairs and hardware modifications page. If not, you'll likely need to get it repaired. Perhaps a short video of its behaviour would confirm this. What is the display showing during this? Is there a fault code showing? Does it seem to be restarting all the time? Quote Link to comment Share on other sites More sharing options...
Leondavibe Posted February 7, 2023 Share Posted February 7, 2023 (edited) On 2022/11/13 at 8:15 AM, Joséhartz said: My inverter keeps on screaming and when I reset it, all the loghts flashes and still keeps on screaming with all the lights flashing. What can I do? please help. HYBRID SOLAR INVERTER MODEL SYSV18-5K MPK if you say reset do you mean reset settings or reboot (switch off -on) what batteries do you have connected? i would start with a default settings hold the esc (6 secs) button it goes into the reset menu 2 options the one with rst only option with s in the middle is the reset option that is changed via +- centre buttons hold enter it will reboot and reset to default settings if you have a lithium battery connected be sure to soon after enter the settings and change to correct for your battery 14 battery type LI or USE (user settings) 17 bulk charge voltage 18 float voltage 19 low dc cut-off voltage 20 batter sop discharge when grid avail to keep reserve for shedding 21 battery stop charge voltage with your correct settings to prevent it from over charging on whatever the default battery config is from what i understand of menu options 00 exit settings menu 01 output source priority 02 ac input range 03 output voltage 04 output freq 05 solar supply priority 06 overload bypass enable/disble 07 auto restart on overload 08 auto restart overtemp 09 solar energy grid feed 10charge priority cso (utility only when no solar) snu solar and util same time oso solar only 11 max combined charge amps 13 max utility charge 22 auto page turn on display 23 backlight control 24 alarm control 25 beeps when primary source interupt 27 record fault code Edited February 7, 2023 by Leondavibe more info Quote Link to comment Share on other sites More sharing options...
Leondavibe Posted February 7, 2023 Share Posted February 7, 2023 (edited) On 2018/04/21 at 7:26 AM, Anarchy05 said: Hi Guys, Could you please assist me in helping a friend, he has an off grid system,on a remote farm. He has a Synerji 5kva,with 9 300w panels,3 in series,connected to 3 in parallel. The inverter is then connected to 8 205ah batteries,also HA-02 per 4 batteries. The issue is that the batteries don't fully charge in one day. And he has to get up at 2-3 in the mornings to start the generator. The loads he has are a box deep freezer and a TV in the house. The lights all run from a 12v system that is separate. I don't know what else to do for him anymore to try and assist leaving this here in case someone lands here with same question in the settings of these synerjy inverters the max charge amps can be set in menu item 11 i would first check that this is at least equal to the minimum of the mppt to make sure it charges at the max it could and menu item 5 deals with priority of what to do with solar power ie LBU load battery utility or BLU battery load utility and menu item 10 is to select what charges battery solar first then utility if no solar or combinantion of solar and utility same time or solar only Edited February 7, 2023 by Leondavibe adding more info Quote Link to comment Share on other sites More sharing options...
Andy Boom Posted Thursday at 02:37 Share Posted Thursday at 02:37 Hi I've got a Synergy 5KVA Inveter but there are no markings for positive or negative Quote Link to comment Share on other sites More sharing options...
Beat Posted 2 hours ago Share Posted 2 hours ago (edited) On 2024/09/12 at 4:37 PM, Andy Boom said: Hi I've got a Synergy 5KVA Inverter but there are no markings for positive or negative I have 2 Synergji/Axpert MKS 5K inverters, but no problem to identify + and - Battery connections. It's also in the manual. Edited 2 hours ago by Beat Quote Link to comment Share on other sites More sharing options...