Axpert 5kW high load immediately after power cut


hjlinde

Recommended Posts

Hi there, 

Trying to understand whether this is normal or not... I have a 5kW Synapse KRM+ inverter - it's wired into DB and all. Everything is working, inverter runs in ECO/Bypass mode - not online mode.

Something i've noticed is that, lets say i'm currently drawing 450W continuous in the house - load-shedding kicks in, suddenly the inverter shows the load is 1.2kW in the house, the fans spin up and less than 10s later it goes back to the 450W it was providing previously. Is this normal? If not or if so, what is the reason for it? 

Link to comment
Share on other sites

On 2023/05/30 at 12:37 PM, hjlinde said:

load-shedding kicks in, suddenly the inverter shows the load is 1.2kW in the house, the fans spin up and less than 10s later it goes back to the 450W it was providing previously. Is this normal? If not or if so, what is the reason for it? 

Yes, it could in effect be the fridge and freezer, as @madness_za mentioned. The switching over from battery to line mode may take up to 20ms, enough for some compressors to stop, depending on the size of their flywheel. They then try to restart and that takes a high current. The display of the inverter and Watchpower as well have some time lag after incidents.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...