hjlinde Posted May 30, 2023 Share Posted May 30, 2023 Hi there, Trying to understand whether this is normal or not... I have a 5kW Synapse KRM+ inverter - it's wired into DB and all. Everything is working, inverter runs in ECO/Bypass mode - not online mode. Something i've noticed is that, lets say i'm currently drawing 450W continuous in the house - load-shedding kicks in, suddenly the inverter shows the load is 1.2kW in the house, the fans spin up and less than 10s later it goes back to the 450W it was providing previously. Is this normal? If not or if so, what is the reason for it? Quote Link to comment Share on other sites More sharing options...
madness_za Posted May 31, 2023 Share Posted May 31, 2023 I've seen similar spikes but because my fridge and freezer are kicking on for a second. Quote Link to comment Share on other sites More sharing options...
Beat Posted June 1, 2023 Share Posted June 1, 2023 On 2023/05/30 at 12:37 PM, hjlinde said: load-shedding kicks in, suddenly the inverter shows the load is 1.2kW in the house, the fans spin up and less than 10s later it goes back to the 450W it was providing previously. Is this normal? If not or if so, what is the reason for it? Yes, it could in effect be the fridge and freezer, as @madness_za mentioned. The switching over from battery to line mode may take up to 20ms, enough for some compressors to stop, depending on the size of their flywheel. They then try to restart and that takes a high current. The display of the inverter and Watchpower as well have some time lag after incidents. Quote Link to comment Share on other sites More sharing options...