Axpert VM III

Featured Replies

TL;DR: the power factor is indeed extremely low and my unit consumes very close to 50W at standby (not 35W as stated in the datasheet)

I recently bought a RCT Axpert VM III-3000-24. Upon my initial power measurements I was very concerned about the standby power usage as my clamp current meter was measuring between 1.2A and 1.3A. Upon reading this thread I decided to invest in two Kill-A-Watt units to measure the true power usage.

I currently have no solar and am running this simply as a backup UPS. After running one on the AC input and one on the inverter output I can now share my results.

  • Total test run time: 7d 10h
  • Total power in: 34.7kWh
  • Total power out: 25.2kWh
  • Ave load: 140W
  • Max load: 700W
  • Min load: 30W
  • Inverter standby power: < 50W (AC in and battery, doesn't seem to make much difference)
  • Inverter power factor with no load: 0.17

Attached are images of the power factor and standby power usage over one hour.

IMG_20200821_182830.jpg

IMG_20200821_182822.jpg

  • 4 months later...
  • Replies 101
  • Views 47.4k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • Well they call it an Axpert, but it is a Hybrid inverter (hence the no-battery option) so it is probably more like the next-Gen Infini. So they have an "InfiniSolar V" which is more like an Axpert, an

  • I think you need to realize you are a bit biased. There are many manufacturers of cheap inverters and people aren't just jumping on that band-wagon. The Axpert inverters are actually incredi

  • pilotfish
    pilotfish

    This Inverter looks awesome, I WANT! Had a quick glance at the user guide, 5kVA version adds the following; 5000VA / 5000W inverter 4000W 500V MPPT BMS comms for LiFe04

Posted Images

Hi guys!
I have an Axpert VMIII 5Kw. No solar, just batteries - used as a backup UPS for the house. Do you know why it shuts down on overload while in the bypass mode? Why would it care? Is there a way to stop it from rebooting on overload while in bypass?

Before this model I had a 5Kw MKS and it continued to work overloaded in bypass with no issues.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.