14 minutes ago, gabriel said:

do you think it will be able to keep the batts at 100% soc?

Seems like it was designed to do so. Although the charging amps stated in the Data sheet is not what I would expect for a 250Ah battery, I guess they have designed it for keeping the battery at 100% SOC with an Occasional discharge.

1672952342_Gabrile1.PNG.96a2c612e460422eaeb4003289e74bf1.PNG

The adjustable Trickle voltage meets the standby volts of your Sonic's, but the Quick Charge voltage is a bit lower than the Cycle voltage of the Sonic's.. 

1890154283_Gabriel2.PNG.970d60b50c600303cb544aa4eff72c9f.PNG

I guess it will function well as a backup.. 

 

 

Link to comment
Share on other sites

On UPS'es, the larger ones, the charge current is the marker.

What this means  (copied from the spec sheet), on a 36v bank, I'm not sure: 11A at normal line & normal temperature (Average) 5000 - 30A

Rule of thumb: On a 12v inverter:
100ah battery, you need min 10amps.
200ah battery, min 20amps.

etc.

Link to comment
Share on other sites

4 hours ago, gabriel said:

hi gents, what is your take on this ups, see attached. i have 3 good 250ah sonic agm batteries which i would like to use with it. do you think it will be able to keep the batts at 100% soc? is the price of 7k [ex batteries and vat]  for the 3kva unit too high?

thanks in advance! :)

Tescom-SSPro-range 2017-Jan (9).pdf

You may want to consider going for the Axpert King. It is effectively a online UPS. Comes in both a 3kVA (24v) and 5kVA (48v).

Link to comment
Share on other sites

7 hours ago, Gnome said:

You may want to consider going for the Axpert King. It is effectively a online UPS. Comes in both a 3kVA (24v) and 5kVA (48v).

I think Gabriel is trying to utilize 3x batteries after 1 failed if memory serves correctly.

12 hours ago, gabriel said:

hi gents, what is your take on this ups, see attached.

I used the same inverter for a long time which I installed when the rolling blackouts started to bite - it was great. I initially used a different unit which would often cause my PC's/TV's/Amps etc to restart at changeover but that stopped when replaced with this inverter. I removed it when I installed the PV system and it is now resting in my storeroom.

The 5kVA unit has a 30A charger which is perfect for your bank - don't forget the battery balancer!

Link to comment
Share on other sites

11 minutes ago, pilotfish said:

it is now resting in my storeroom

would you consider active service for it again? :)

edit... you just mentioned it is the 5kva unit and 48v, so i cant use it...

 

11 minutes ago, pilotfish said:

I think Gabriel is trying to utilize 3x batteries after 1 failed if memory serves correctly.

jip, you're right. i now have 3x250ah monsters which in series will give 36v and can be used with an ups in my wife's practice. as power outages are not a daily occurrence i believe the batteries should last long in that environment. regarding the battery balancer, yes, i still have one and it will be used.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...