Posted November 22, 20186 yr Hi Forum, I have a safari camp in Malawi with 3 separate off grid systems as the 3 areas are quite a long way from each other. I would like to start with the largest one which has 2 AXPERT 5kva Inverters with 5 - 6 Pylontech batteries and 4 "strings" of PV panels. I want to ensure longevity of the batteries while getting maximum efficiency out of the system. The settigs are as follows: 01 UtI 02 . 30a 03 . APL 04 . NOi- 05 . USE 06 . LtE 07 . ttE 11 . 30A 12 . 47v 13 . 48v 16 . SnU23 . byE 26 . 53.2v 27 . 52v 29 46v 31 56E Any comments would be greatly appreciated. Thanks, Chris
November 22, 20186 yr Hi Chris 5 Pylontechs can easily handle 125A charging so you could set charging to 50A for each inverter and not compromise your batteries. I would install ICC and buy the communication cable for Pylontechs so that you can monitor your system. You may not be able to load to the cloud but a record of how your system behaved on a particular day is invaluable. Setting 27 can be a little higher 52.8V thereabouts. The Pylons BMS does some syncing but only at 95% full (52.0 V) might be too low - I cannot remember). Setting 12 should be 48V and Setting 13 should be 51V but in an off-grid system it is a moot point. Setting 29 should be 47.5V (SOP for Pylons and Axperts).
January 8, 20196 yr Author The "Axpert" inverters come with software called WatchPower. I have downloaded it to PC (Windows 10) and it does not communicate with the Inverter. Perhaps it needs another driver? is this software comparable to ICC and if not, is it possible to download ICC from the internet that will work on Apple Mac? Thanks in advance, Chris
January 9, 20196 yr Hi Chris WatchPower is not the greatset software. ICC is avilable as a Windows product of for a Raspberry Pi. I ran the Windows version for nearly two years but recently moved over to a headless RPi. This has the advante that you can still view your data on your MAC.
January 9, 20196 yr Author Hi Chris, Thanks again for your informative reply. As mentioned earlier, we have 3 separate solar systems. Will I be able to use the same software for Raspberry PI with all 3 systems and just plug into the inverter of any one of them?
January 10, 20196 yr 3 separate systems I would then have 3 separate Rpis . Data logging is a 24/7 business. If something were to go wrong I would want data in the period before the failure. I have 2 inverters running of 1 Pi but the two inverters are in parallel.
January 11, 20196 yr Author Wow OK. I am hoping that I will only need to buy ICC once that can be used on all 3 systems? I have 2 systems each with 2 inverters in parallel and one with one inverter.
November 27, 20195 yr Author Hi Forum, Going back to the settings on the off-grid Axpert inverters with Pylontech US2000 plus described above, I now have the following questions: 27 Floating charging voltage: This is set at 52.8v but does it apply with the set up as I read that LiFE batteries do not like a trickle charge? 26 Bulk charging voltage: What is the maximum this should be set at without stressing the batteries? 29 Low DC cut-off voltage: Chris said that SOP is 47.5 V for Axperts and Pylontechs but often the Axperts show a warning light for low cut-off when batteries LEDs are around 50% charged and the Axperts are showing a voltage of around 49v. Thanks in advance for any feedback.
November 27, 20195 yr 4 hours ago, Chris Buckley said: 27 Floating charging voltage: This is set at 52.8v but does it apply with the set up as I read that LiFE batteries do not like a trickle charge? 26 Bulk charging voltage: What is the maximum this should be set at without stressing the batteries? Use 52.0 and 52.5 V, as per Youda's excellent post here, giving reasoning: https://powerforum.co.za/topic/2322-youdas-off-grid-lab/?do=findComment&comment=64125
November 27, 20195 yr 6 hours ago, Chris Buckley said: 29 Low DC cut-off voltage: Chris said that SOP is 47.5 V for Axperts and Pylontechs but often the Axperts show a warning light for low cut-off when batteries LEDs are around 50% charged and the Axperts are showing a voltage of around 49v. ICC would solve this problem since it gets the SOC accurately from the pylons and tells the axperts what to do.
November 28, 20195 yr Author The problem is I have 3 separate systems as follows: 1. 24 x 295w Canadian solar PV with 6 x US2000 Plus Pylontech and 2 x 5KVA Axperts 2. 18 x PV as above with 5 x Pylontech and 2 x 5KVA Axperts 3. 12 x PV as above with 3 x Pylontech and 1 x 5KVA Axpert The cost of 3 ICC kits is expensive and not sure I need all that info to plough through. Or does one only need to look through it once there is a problem? Would the cable by itself not help with the communication between batteries and axperts?
November 28, 20195 yr Author 20 hours ago, Coulomb said: Use 52.0 and 52.5 V, as per Youda's excellent post here, giving reasoning: https://powerforum.co.za/topic/2322-youdas-off-grid-lab/?do=findComment&comment=64125 Sorry for being so thick but is 52v for 27 Floating charging voltage or 26 Bulk charging voltage?
November 28, 20195 yr 24 minutes ago, Chris Buckley said: 52v for 27 Floating charging voltage or 26 Bulk charging voltage? Float has to be the lower of the two; you can't enter them the wrong way around. So 52 V for float (setting 27), 52.5 V for bulk/absorb (setting 26).
November 28, 20195 yr Author 8 minutes ago, Coulomb said: Float has to be the lower of the two; you can't enter them the wrong way around. So 52 V for float (setting 27), 52.5 V for bulk/absorb (setting 26). 20 hours ago, Coulomb said: Use 52.0 and 52.5 V, as per Youda's excellent post here, giving reasoning: https://powerforum.co.za/topic/2322-youdas-off-grid-lab/?do=findComment&comment=64125 Sorry for being so thick but is 52v for 27 Floating charging voltage or 26 Bulk charging voltage?
November 28, 20195 yr 3 hours ago, Chris Buckley said: The problem is I have 3 separate systems as follows: 1. 24 x 295w Canadian solar PV with 6 x US2000 Plus Pylontech and 2 x 5KVA Axperts 2. 18 x PV as above with 5 x Pylontech and 2 x 5KVA Axperts 3. 12 x PV as above with 3 x Pylontech and 1 x 5KVA Axpert The cost of 3 ICC kits is expensive and not sure I need all that info to plough through. Or does one only need to look through it once there is a problem? Would the cable by itself not help with the communication between batteries and axperts? ICC is currently the only way to get the axperts and pylons talking to each other. Without ICC you effectively half your battery capacity. ICC reads the SOC from the pylons and tells the axperts what it is. Those expensive pylons are only being drawn down halfway without ICC.
November 28, 20195 yr Author So does it follow that until I get the ICC software installed, while the Axperts are not getting correct SOC from the Pylons that I should temporarily keep the settings of 52.8v and 53,2v for 27 and 26 respectively rather than further reduce the range of the batteries by applying the new settings of 52v and 52.5v?
November 28, 20195 yr 4 hours ago, root said: ICC is currently the only way to get the axperts and pylons talking to each other. Without ICC you effectively half your battery capacity. ICC reads the SOC from the pylons and tells the axperts what it is. Those expensive pylons are only being drawn down halfway without ICC. Why do you say that? Can't a BMV 700/702/712 be connected onto Pylon batteries?
November 28, 20195 yr 11 minutes ago, GVC said: Why do you say that? Can't a BMV 700/702/712 be connected onto Pylon batteries? Don't know the blue stuff. But given that the OP uses axperts its unlikely that a BMV wil work in his setup.
November 28, 20195 yr I was asking because I am using a BMV 702 on my Lithiums with an Axpert (no extra cable). The software I use reads the battery voltage, SOC, Amps, Watt etc. from the BMV and regulates the inverter accordingly. I however don't know the Pylons and don't know how difficult it would be to connect a BMV to them...I mean they do use those plug connectors..