Voltageza Posted September 8 Share Posted September 8 Hi guys Need a little help in calculating the bus-bar size for a project. (See image attached) 9 x 15000kva Victron Qautro's 4 x 450/200 MPPTs 3 x 60/48 Freedom Won Batteries. 1000A Discharge The red line is the busbar. Dark Blue Freedom Won Batteries Light Blue/Cyan Inverters Green MPPTs We calculated that a 1000A busbar will do the job but going with 1200A for safety. What are your calculations on this setup please? Thanks JAKE LAYOUT.pdf Quote Link to comment Share on other sites More sharing options...
WannabeSolarSparky Posted September 8 Share Posted September 8 (edited) Copper - 50mm X 20mm X length = should give you 1200amp at 52v nominal DC https://www.allumiax.com/bus-bar-size-calculator https://www.em.co.za/site/Catalogue PDFs/2020-Charts _ Tables.pdf Edited September 8 by WannabeSolarSparky zsde 1 Quote Link to comment Share on other sites More sharing options...
TaliaB Posted September 8 Share Posted September 8 (edited) 2 hours ago, Voltageza said: Hi guys Need a little help in calculating the bus-bar size for a project. (See image attached) 9 x 15000kva Victron Qautro's 4 x 450/200 MPPTs 3 x 60/48 Freedom Won Batteries. 1000A Discharge The red line is the busbar. Dark Blue Freedom Won Batteries Light Blue/Cyan Inverters Green MPPTs We calculated that a 1000A busbar will do the job but going with 1200A for safety. What are your calculations on this setup please? Thanks JAKE LAYOUT.pdf 73.51 kB · 2 downloads 50 x 20mm will work this is what i use 100mm x 10mm you will have to pre order and expensive https://goldcirclemetals.co.za/copper-busbar/ https://acdc.co.za/terminals-insulators-busbar-supports-flex-solid-busbar/4509-100x10mm-solid-copper-busbar-3m-length.html?srsltid=AfmBOopiimEXBMhohEUDJ0a1FB3aENbgHEddrM228z_nxd5E-nJji8_r Edited September 8 by TaliaB WannabeSolarSparky 1 Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted September 8 Share Posted September 8 2 hours ago, TaliaB said: 50 x 20mm will work this is what i use 100mm x 10mm you will have to pre order and expensive https://goldcirclemetals.co.za/copper-busbar/ https://acdc.co.za/terminals-insulators-busbar-supports-flex-solid-busbar/4509-100x10mm-solid-copper-busbar-3m-length.html?srsltid=AfmBOopiimEXBMhohEUDJ0a1FB3aENbgHEddrM228z_nxd5E-nJji8_r I take it that the load could be 135kVA and 2600A if inverters operate at full capacity at 52V. WannabeSolarSparky 1 Quote Link to comment Share on other sites More sharing options...
TaliaB Posted September 8 Share Posted September 8 18 minutes ago, Scorp007 said: I take it that the load could be 135kVA and 2600A if inverters operate at full capacity at 52V. You are 100%correct with common rail busbar for 9 x15kva inverters you will need 101,6 X 25,4 busbar to support full load current of 2600A. Thanks @Scorp007 for the correction. The above size copper busbar will entertain 3000A WannabeSolarSparky 1 Quote Link to comment Share on other sites More sharing options...
Voltageza Posted September 8 Author Share Posted September 8 Hi Guys Thanks for the input. Our argument is that at no point of connect 2600A will be drawn. Loads are evenly spread. The highest point drawn will be at the battery connection and that is a 1000A. It all the inverters were connected together at one point it will be a different scenario. I also read somewhere that installing the MPPTs between the inverter and not all at one end will also balance the loads. We arranged a meeting with a engineer to get more clarity. PS: We order our busbars from Copalcor in PE. Quote Link to comment Share on other sites More sharing options...
Scorp007 Posted September 8 Share Posted September 8 2 hours ago, Voltageza said: Hi Guys Thanks for the input. Our argument is that at no point of connect 2600A will be drawn. Loads are evenly spread. The highest point drawn will be at the battery connection and that is a 1000A. It all the inverters were connected together at one point it will be a different scenario. I also read somewhere that installing the MPPTs between the inverter and not all at one end will also balance the loads. We arranged a meeting with a engineer to get more clarity. PS: We order our busbars from Copalcor in PE. Although it sounds a good solution to say the equipment will be used at 1000/2600A=38% anyone can after installation decide to double the load as the system can do it. Equipment is always installed with a safety margin at full capacity. Steve87 1 Quote Link to comment Share on other sites More sharing options...