"Hello, I have a Triple A inverter (Voltronic axpert VM 3) and felicity 200 48  and I’m getting the 'BP' error at different times. Sometimes it happens once a day, sometimes once a month. Sometimes, the alarm beeps, the error code appears, and then it beeps again, the code disappears, and the screen goes back to normal. Other times, I wake up to find the inverter completely turned off.

Two weeks ago, I woke up and everything was working fine, but I noticed the battery voltage was around 24V, even though my battery setup is 48V. The system was functioning normally and the loads were running, but the inverter wasn’t charging the battery.

I updated the firmware to 60.76, and the problem disappeared.

This morning, I woke up and found it turned off again."

I turned it on , everything is normal except having wrong time in the logs on the mobile application 

 

anyone has an idea why it turns off ?

Edited by esmail-kassir
Link to comment
Share on other sites

2 hours ago, TaliaB said:

bP" is the "Battery not Present" error.

BMS would have disconnected the battery due to too high or too low battery voltage. 

Theoretically you are 100 % correct 

but I tend to believe this is firmware bug , as it coexists with other strange behavior. Also the battery screen doesn’t show any warning icons or messages . And it happens out the peak usage hours ( actually it didn’t happen during any moment where the load ir temperature where high) 

Link to comment
Share on other sites

22 hours ago, esmail-kassir said:

Two weeks ago, I woke up and everything was working fine, but I noticed the battery voltage was around 24V, even though my battery setup is 48V. The system was functioning normally and the loads were running, but the inverter wasn’t charging the battery.

The VM series saves a little money by having one firmware for both 24 V and 48 V models. It decides which hardware it is running by reading the voltage on a pin at power-up. The result is stored in RAM; I think it's static RAM but it might be dynamic. In either case, a glitch in the power supply could cause the RAM contents to change, making it think that it's running on the wrong hardware. This can be very bad; I would always restart immediately if that happens.

Though possibly the problem could happen due to a comms error that happened to fluke a good CRC. The display remembers what the nominal voltage of the system is from the results of the last QPIRI command. That's far less dangerous. You could find out if it's the display or the inverter itself by unplugging and re-plugging the RJ-45 cable from the removable display (not so easy if you happen to have a model with the round/colour display). Warning: this will effectively switch off the main switch, which will drop the loads. Reconnect the display before the inverter completely shuts down; it should not shut down if you have a charging source (AC-in or PV).

A few screws should make this RJ-45 cable accessible.

If it's the removable display firmware, then updating that may fix the problem.

Link to comment
Share on other sites

1 hour ago, Coulomb said:

The VM series saves a little money by having one firmware for both 24 V and 48 V models. It decides which hardware it is running by reading the voltage on a pin at power-up. The result is stored in RAM; I think it's static RAM but it might be dynamic. In either case, a glitch in the power supply could cause the RAM contents to change, making it think that it's running on the wrong hardware. This can be very bad; I would always restart immediately if that happens.

Though possibly the problem could happen due to a comms error that happened to fluke a good CRC. The display remembers what the nominal voltage of the system is from the results of the last QPIRI command. That's far less dangerous. You could find out if it's the display or the inverter itself by unplugging and re-plugging the RJ-45 cable from the removable display (not so easy if you happen to have a model with the round/colour display). Warning: this will effectively switch off the main switch, which will drop the loads. Reconnect the display before the inverter completely shuts down; it should not shut down if you have a charging source (AC-in or PV).

A few screws should make this RJ-45 cable accessible.

If it's the removable display firmware, then updating that may fix the problem.

The 24 issue occurred once and never happened again 

but I still have the sudden shutdown issue and or BP Fault only when PV availability 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...