Recommended Posts

Hi,

I need to power around 8 KW of equipment at my office, the cheapest design i have been able to come up with is 2 x 5w Axpert Inverters in Parallel with the linked to 5 x 3.5KW  Pylontech batteries, has I have installed a number of Single Axpert units with the Pylontech batteries, I am unsure how the Parallel units would cope ? technically would only 1 Axpert charge the batteries ?

Please any advice would be appreciated.

Thanks

Link to comment
Share on other sites

1 hour ago, Dean said:

technically would only 1 Axpert charge the batteries ?

You can set separate charge limits on each, but generally you'd have each do about the same utility charging (maybe you'd have 40 A on one and 30 A on the other since you can't set a 35 A limit). If you have solar panels, you can put them all on one or split them between the two.

8 kW is quite a load. Is it all constant, like computer servers? Or are there motors with heavy start-up requirements?

8 kW continuous on a 10 kW rated system leaves little room for surges.

[ Edit: is it all on one phase? ]

Edited by Coulomb
Link to comment
Share on other sites

Thanks, the load will only be around a constant 5-6 with (4 in spare for any inrush current) Its single phase.

If I wanted to put 7-8kw of solar into the mix, would you go directly to both axperts units or would you AC couple with another inverter.

Thanks

 

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...