Hi All

I have 2 x 5kwh Freedom Won batteries and 8kw Sunsynck inverter. I have a switch over on my Eskom Incomer circuit breaker. I want to charge my batteries using my 7500w Ryobi generator by just switching over to generator at the Eskom main incommer. I adjusted my battery charging amps to 10A and switched over but my Inverter showed grid as 0w and had no response.

Is it possible to charge my batteries using my generator connected to the main incomer and how do I go about it?

Thanks

What's the frequency and voltage on the output side of the generator? Under a load. Most inverters in SA will be set for the SA grid code, so if voltage or frequency varies too much the inverter will ignore the generator. The inverters do this for incoming mains as well.

  • 2 months later...
On 2025/04/04 at 1:57 PM, Sidewinder said:

@Francois Taljaard ,

Isn't a Genny supposed to be connected via the AUX port? That's what I thought it can be used for. Other than driving Loads via settings.

Just read up about the settings.

Yes, it is... but then you cannot have any loads also connected to it at the same time - it's either "in" or "out".

1 hour ago, HennieL said:

Yes, it is... but then you cannot have any loads also connected to it at the same time - it's either "in" or "out".

True that... Any load that you currently have on the "Aux" port, could either be moved to "Essentials" side (and controlled via a Wifi Switch) or

Move then to the "Non-Essectial" side, so they only work from Solar when Grid is available i.e. just before the CT-coil location.

Then the "Aux" port is free to use as "In" port permanently for Genny, Micro Inverters, or even Wind power.

  • 3 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...