___ Posted August 15, 2019 Share Posted August 15, 2019 (edited) 12 minutes ago, CarlT said: why take the chance? I agree. If you can add a measure of protection by not oversizing the fuses, why not 12 minutes ago, CarlT said: From Pylontech's datasheets, the US2000 has a recommended charge/discharge current of 25A and a max charge/discharge current of 50A, while the US3000 has 37A and 74A respectively. Ideally your fuse will blow before you reach these maximums. No, that is way too soon. The datasheet shows a recommended maximum CONTINUOUS discharge value of roughly C/2, but it also shows a peak of 100A (2C) for 15 seconds. This is the rating you want to protect against, so I would size the fuse at 100A or even at 125A. That is half of the 250A recommendation of earlier, so I am still agreeing with you broadly Edit: It has to be noted though, that's for a SINGLE module. 250A would be the right size fuse for two modules, but I would also consider the max draw from the inverter, for example a 3KVA inverter at 50V (ish, cause it makes the math easier) can only peak at 6kva and will only draw 120A for about a second, so again it probably makes no sense to go above 125A or maybe 150A, and you add a little bit of safety. Edited August 15, 2019 by plonkster Quote Link to comment Share on other sites More sharing options...
Ingo Posted August 15, 2019 Share Posted August 15, 2019 I don't know where the 250A recommendation came from but if it was from my post then I want to apologize for it not being clear. The statement was made that Mersen is not rated for DC, I merely commented that my Mersen is rated for 220V and 250A DC, I did not say that you need a 250A fuse in there. Sanity should still prevail as Plonkster pointed out with the 125A/150A fuse suggestion. ___ 1 Quote Link to comment Share on other sites More sharing options...
___ Posted August 15, 2019 Share Posted August 15, 2019 1 minute ago, Ingo said: Mersen is rated for 220V and 250A DC They have different size holders. The 160A holder I have cannot take 200A fuses for example. But they are definitely DC rated! Ingo 1 Quote Link to comment Share on other sites More sharing options...
Ingo Posted August 15, 2019 Share Posted August 15, 2019 2 minutes ago, plonkster said: They have different size holders. The 160A holder I have cannot take 200A fuses for example. But they are definitely DC rated! Yes. I just have the next size up. ___ 1 Quote Link to comment Share on other sites More sharing options...
CarlT Posted August 15, 2019 Share Posted August 15, 2019 4 minutes ago, plonkster said: I agree. If you can add a measure of protection by not oversizing the fuses, why not No, that is way too soon. The datasheet shows a recommended maximum CONTINUOUS discharge value of roughly C/2, but it also shows a peak of 100A (2C) for 15 seconds. This is the rating you want to protect against, so I would size the fuse at 100A or even at 125A. That is half of the 250A recommendation of earlier, so I am still agreeing with you broadly The problem is slightly more complex than most people realise. Unfortunately it isn't as easy as saying "pick a fuse that will blow at X amps". Here is a picture of the current-time characteristics from one of the Jean Muller DC fuses: So if we agree that 100A for 15s is the limit that we don't want to exceed, then we need to choose from the fuse values that fit inside the box I drew (time on the Y-axis, current on the X-axis, graph is logarithmic). But we need to be careful that the fuse we choose don't blow too quickly. For example, if we operate at the recommended currents of 37A (for the US3000), we can't use the 20A fuse, since it will blow at around 11s. The 100A fuse might last indefinitely at 37A, and even last 10 000s at 100A, so that might not work. The 40A or 50A fuse might be a good compromise. Cef and ___ 1 1 Quote Link to comment Share on other sites More sharing options...
___ Posted August 15, 2019 Share Posted August 15, 2019 3 hours ago, CarlT said: For example, if we operate at the recommended currents of 37A (for the US3000), we can't use the 20A fuse, since it will blow at around 11s. The 100A fuse might last indefinitely at 37A, and even last 10 000s at 100A, so that might not work. The 40A or 50A fuse might be a good compromise. You went one step further and looked at the actual chart, which I didn't do, so you're absolutely correct. Nice graph too! I still think that I would rather let the BMS make the call for currents that are technically within the capability of the battery, for example even a 4C current (200A) for a second is not really a reason to pop a fuse, which would mean the 80A fuse is the one to go for. But broadly we are in agreement. You really can get away with a much smaller fuse, and it adds safety. CarlT 1 Quote Link to comment Share on other sites More sharing options...
CarlT Posted August 16, 2019 Share Posted August 16, 2019 15 hours ago, plonkster said: You went one step further and looked at the actual chart, which I didn't do, so you're absolutely correct. Nice graph too! I still think that I would rather let the BMS make the call for currents that are technically within the capability of the battery, for example even a 4C current (200A) for a second is not really a reason to pop a fuse, which would mean the 80A fuse is the one to go for. But broadly we are in agreement. You really can get away with a much smaller fuse, and it adds safety. The Jean Muller fuses are nice, but it seems the local agents don't import them. Everyone uses the AC fuses! I am cautious by nature, so in my list of priorities, first is the safety of my family, followed by the protection of the equipment. Quote Link to comment Share on other sites More sharing options...
___ Posted August 16, 2019 Share Posted August 16, 2019 7 minutes ago, CarlT said: The Jean Muller fuses are nice, but it seems the local agents don't import them. Everyone uses the AC fuses! I can't say I've had this experience. I got the Mersen holder and fuse right in the beginning. It has a DC rating. Sure, I couldn't just buy it at the local AC/DC, I had to actually order it from Rubicon... Quote Link to comment Share on other sites More sharing options...
FixAMess Posted January 19, 2020 Share Posted January 19, 2020 So, is the recommended fuse size for 3.5KW Pylontechs 50A fuses? I just bought 125A fuses.... Quote Link to comment Share on other sites More sharing options...
VisN Posted January 19, 2020 Share Posted January 19, 2020 32 minutes ago, FixAMess said: So, is the recommended fuse size for 3.5KW Pylontechs 50A fuses? I just bought 125A fuses.... I'm running 2 x US3000s on 125A Jean Muller fuses, I'd be interested in the answer to this question as well. Quote Link to comment Share on other sites More sharing options...
ColinR4 Posted February 8, 2020 Share Posted February 8, 2020 On 2020/01/19 at 11:13 AM, VisN said: I'm running 2 x US3000s on 125A Jean Muller fuses, I'd be interested in the answer to this question as well. I'm Sure you are spot on at 125A DC fuse for 2 Pylon 3.6KW VisN 1 Quote Link to comment Share on other sites More sharing options...
Hoang Posted June 5, 2020 Share Posted June 5, 2020 Do you guys notice that the DC cable out of pylontech can only take 120A max? Quote Link to comment Share on other sites More sharing options...
Tsa Posted August 28, 2020 Share Posted August 28, 2020 So just for clarity on this. With the Lithiums out there (Pylon/Dyness) which have their own switches and also BMS to handle any surge issues. Does one still need, by regulations, a battery disconnect and fuse? Agreed it is good practice, BUT is it law in terms of SANS and Insurance? Quote Link to comment Share on other sites More sharing options...
___ Posted August 28, 2020 Share Posted August 28, 2020 You should always think about failure modes, belts and suspenders. What happens if just one of the big old FETs (which many use now) is damaged and the battery does NOT disconnect in a timeous fashion? Then you want a safe part of the connection to burn out rather than an unsafe part, that is to say, you want the fuse to blow and not the copper cable. I have a similar situation inside my coffee maker. It has a combination thermal fuse and thermal switch (aka klixon) device which costs like 12 Euros. One could argue, why have the fuse? The Klixon part already interrupts the current if something bad happens. And the answer would be, because the klixon could fail, and then you want a backup. Of course my beef with this particular Siemens coffee maker is that the thermal fuse blows before the klixon interrupts things whenever the water pump delivery is low... which is just terrible design. The fuse should blow as a last resort... not the other way round! Quote Link to comment Share on other sites More sharing options...
Tsa Posted August 28, 2020 Share Posted August 28, 2020 Thanks and agreed 100%, but again my question is more directed to the legality of an install. Specifically how complete the install is as supplied by the installer. If the cable melts and burns down the house, will the insurance say, no game, you didn't have your fuse installed as determined by the regulations. If a fuse is all it takes, then just install a mega fuse and holder for instance. Btw this is for 3x 2.4 Dyness and would be looking at 125A fuse. That or the Keto with 125A. Quote Link to comment Share on other sites More sharing options...
___ Posted August 28, 2020 Share Posted August 28, 2020 (edited) 23 minutes ago, Tsa said: If the cable melts and burns down the house, will the insurance say, no game, you didn't have your fuse installed as determined by the regulations. Why would you take the chance? But okay, you're right, I'm arguing the sensibility and you're arguing the legality... so here goes... That's from a draft copy of SANS-10142-1 that has the new DC bits added to it. It says you MUST have an overcurrent device in place. Does not have to be a fuse, can be a breaker, but it must be able to interrupt the full short circuit current of the the battery (which would be a very hefty breaker). The insurance company will smack you on the letter of the regulations. Put the damn fuse in What is also interesting here is how ground-faults are avoided. The cable between the battery and the protection device (fuse) must be kept as short as possible, and the positive and negative cabling up to the fuse must be kept separate. They are clearly trying to avoid fault conditions on the wrong side of the fuse. When you do this, you need a battery fuse only in the positive line, since ground faults are now unlikely (it would have to happen in the very short cable to the fuse on the positive side). Edit: Also note "NOTE 3", which already refers to the battery protective device, aka the BMS. Edited August 28, 2020 by plonkster Tsa, Louisvdw, Cef and 1 other 3 1 Quote Link to comment Share on other sites More sharing options...
Tsa Posted August 28, 2020 Share Posted August 28, 2020 That then makes it 100% clear, thanks @plonkster. So in terms of legality and issuing of CoC on such a system, this SHOULD have been in place. Will do some further reading on SANS -10142-1 on what else "should" have been in place. Next step is decide on and source 125A fuse + holder or go the Keto route. Thanks again Quote Link to comment Share on other sites More sharing options...
Tsa Posted August 28, 2020 Share Posted August 28, 2020 (edited) To add to this. Would this be sufficient protection, or would a normal fuse then be a safer option? https://lithiumbatteriessa.co.za/collections/frontpage/products/1p-dc250v-125a-dc-circuit-breaker or go double and go the Keto route? Edited August 28, 2020 by Tsa Quote Link to comment Share on other sites More sharing options...
___ Posted August 28, 2020 Share Posted August 28, 2020 7 minutes ago, Tsa said: To add to this. Would this be sufficient protection, or would a normal fuse then be a safer option? https://lithiumbatteriessa.co.za/collections/frontpage/products/1p-dc250v-125a-dc-circuit-breaker The critical part is that the breaker must be able to break the full short circuit current of the battery, and for that you need the kA (kilo-Amp) rating of the breaker. It is usually written on the breaker, and is usually something like 3kA, 6kA, or similar. The short circuit current of an LFP battery can exceed 30C (30 times the capacity). On a 100Ah battery, a 3kA breaker would not be enough for example. The fuse is generally a better call in my opinion. It is faster too. A breaker needs 5 times the rated current before it trips instantly. Tsa 1 Quote Link to comment Share on other sites More sharing options...
Rotate Posted August 14, 2021 Share Posted August 14, 2021 Hi All i have x6 UP 5000 batteries. What size Fuses can one then use? Quote Link to comment Share on other sites More sharing options...