Hi Guys,

I have an axpert 3kVA installed in the house with 6 panels and 24V battery, when I tried to connect the air conditioner having 2hp, the inverter shutdown and it doesn't turn on again even in a perfect sunny day.

Can someone help me with this? 

Thank you 

 

Share this post


Link to post
Share on other sites

Try looking @ setting 06 Auto restart when overload occurs. (May have another number, this is from a 5kVA system)

It is disabled by default. So enable it. At least the Inv. should recover then.

Share this post


Link to post
Share on other sites
4 hours ago, Querobin said:

I have an axpert 3kVA installed in the house with 6 panels and 24V battery, when I tried to connect the air conditioner having 2hp

2 hp is over 1500 W, meaning that the start-up surge (if it's not an inverter type) could be as much as 7x that, or over 10 kVA. A typical Axpert has a surge rating of 2x rated output, to 6 kVA. I think the air conditioner is just too big for the inverter.

It sound like you've also tripped some protection somewhere, probably on the battery side to prevent the inverter from coming on.

Hopefully, the inverter hasn't been damaged by the overload. They are supposed to be short-circuit and overload proof, but I'm always wary of testing that.

Check for over 25 V at the inverter battery terminals, and if present see if you can check the internal fuse. It's usually just inside the battery terminals. Note that opening the cover will void your warranty.

Share this post


Link to post
Share on other sites
6 hours ago, Coulomb said:

2 hp is over 1500 W, meaning that the start-up surge (if it's not an inverter type) could be as much as 7x that, or over 10 kVA. A typical Axpert has a surge rating of 2x rated output, to 6 kVA. I think the air conditioner is just too big for the inverter.

It sound like you've also tripped some protection somewhere, probably on the battery side to prevent the inverter from coming on.

Hopefully, the inverter hasn't been damaged by the overload. They are supposed to be short-circuit and overload proof, but I'm always wary of testing that.

Check for over 25 V at the inverter battery terminals, and if present see if you can check the internal fuse. It's usually just inside the battery terminals. Note that opening the cover will void your warranty.

This was my first thought as well. The inverter is probably just too small to run an airconditioner

Share this post


Link to post
Share on other sites
15 hours ago, Coulomb said:

Check for over 25 V at the inverter battery terminals, and if present see if you can check the internal fuse. It's usually just inside the battery terminals. Note that opening the cover will void your warranty.

@Coulomb Thank you for this information. Just to be clear, did you mean I will try to turn on the inverter using batteries above 25V? 

Thanks again.

Share this post


Link to post
Share on other sites
1 hour ago, Querobin said:

did you mean I will try to turn on the inverter using batteries above 25V

I mean your nominally 24 V battery will read over 25 V with a multimeter if it's healthy, so just make sure that you see that 25 V or more at the battery terminals of your inverter. The inverter won't turn on without that.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


Topics

Contact Us - Power Forum South Africa

×
×
  • Create New...