Problems with settings on my Axpert
Good day everyone
I am new to the solar experience. I have just installed a system that consists of 12 X 350W Canadian solar panels connected to a Axpert MKS II 5K inverter.
First I used the system without batteries and it work fine. I then added a Pylontech US3000B battery. I now have a problem setting the bulk charge voltage (which should be 53.2V according to Pylontech ) on the inverter. If I set the setting (program 26) to 53.2V and exit the settings it reverts back to the default setting of 54V.
Anybody with advice how to overcome this issue ?
Have you tried doing the setting on Watch Power .
Hi Chris
No I have not tried that. Will give it a try as soon as I have it set up.
Something else program 05 must be on USE for setting 26 , 27 and 29
Hi Chris
Yes I did set program 5 to use and I can set all the other settings (according to Pylontech) except program 26. I have done it a couple of times but when I exit and go back it is back to the default at 54V.
5 hours ago, Coulomb said:
Is the float setting perhaps at 54 V? You can't have bulk/absorb > float. I believe that they can be equal however.
Good day Coulomb
Thanks for the advise. That was the problem. I have set my float to 52.2V and then I could set my bulk to 53.2V.
Again thank you very much.