I have installed a Axpert MKS Plus 3kVA 2400W 24V Hybrid Inverter  and

Blue nova BN26V-154-4k

No solar panels at present only running off ESKOM for the time being

All household water is from 4 x 1000l rainwater tanks

A 0.75kW pump kicks in when a tap is opend 

When the pump kicks in the Axpert beeps once sometimes twice probably indicating overload??????

This has to relate to the startup of the pump 

The inverter is rated 3kW 

Any views on the subject would be appreciated

Link to comment
Share on other sites

14 hours ago, JohanG said:

A 0.75kW pump kicks in when a tap is opend 

An induction motor's surge current is usually about 7x the rated current. So it will be of the order of 750 x 7 = 5250 VA (with a poor power factor, though starting under load it will draw plenty of real power as well). That's pretty close to the surge rating of the inverter (6000 VA).

Can you check the battery voltage to see if it dips during a startup? A multimeter with a min and max function would be ideal, to catch the instantaneous voltage drop.

Is your wiring up to scratch? 3000 W plus about 10% at 25 V is some 132 A, so your battery cable needs to be able to handle that continuously. You'll need a stout fuse as well. Check for arcing / burn marks on the fuse and fuse holder; perhaps the Nova isn't so good at limiting in-rush current.

It may be possible to suppress the beeps with settings, but first you should ensure that it's not trying to tell you something important.

A new LFP battery will take some time to get its cells all balanced; during that time, it may not get charged fully. So the situation may improve over time.

Link to comment
Share on other sites

On 2019/07/23 at 10:15 AM, JohanG said:

A 0.75kW pump kicks in when a tap is opend 

 

16 minutes ago, JohanG said:

Would installing a pressure tank be a solution

As a rule I install a 60 liter pressure tank for all my clients with pressure pumps when I install solar. Its much kinder to the batteries at night as well. I would recommend it. I prefer them running longer, but less frequent, rather than starting every time you open a tap. 

Link to comment
Share on other sites

  • 4 weeks later...
13 hours ago, DeepBass9 said:

On solar, as Jaco says, it is preferable to have a smaller pump running for longer, than a big pump pulling lots of current for a short time.

yes but that involves a pressure tank, i am basically asking could you do it without a pressure tank but with a smaller motor?

Link to comment
Share on other sites

  • 2 weeks later...

I pump from my borehole to a 5000l pump that feeds the house. The pressure pump I use is on my inverter. I use the DAB Esybox mini 3. It's quite expensive but well worth it. Its an inverter pump, and best of all keeps the pressure the same all of the time. even better than munic supply. As the requirement increases, the pump ramps up.

image.png

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...