Hi guys, I have a 5KVA Axpert inverter and on average, once a week, my load goes over and above the recommended inverter threshold due to various reasons such as the wife and kids putting a toaster on with microwave and airdryer.  My installer mentioned that this should be avoided. My question is will this damage the inverter or does it just automatically switch to grid power?

InkedIMG_2567_LI.jpg

Link to comment
Share on other sites

2 minutes ago, plonkster said:

Most inverters can peak at twice their nominal rating for a second or two. So it really depends on how fast it goes back to the grid. It might be nothing to worry about at all.

Great thanks, its literately for a couple seconds 

Link to comment
Share on other sites

2 minutes ago, Durran said:

Great thanks, its literately for a couple seconds 

My answer of course reflects that it OUGHT to be okay. Jaco has more experience with Voltronic inverters so I am not disagreeing with his experience. He is not the only one who has told me over the years that it is in your interest not to stress them too much. Will it handle the peak? Yes. Is it designed to handle the peak? Yes. Does it stress the inverter more? Yes (that's true for other brands too). Will it shorten the life... again... yes (and also for other brands), so really, there is a design spec somewhere that's perhaps not published for all to see, a design spec that says it must be able to handle this X amount of times.

As an analogy, circuit breakers can handle really high fault currents and safely disconnect them, but they have a specification of how many times it can do it. A cheap breaker can do 2000. An expensive breaker in excess of 10 000.

So yeah... once a week probably fine.

Link to comment
Share on other sites

2 minutes ago, Crankshaft said:

operating a device at or near 100% capacity can't be good long term.

Things will certainly fail quicker if you run them harder. This is true for electronic components too where heat for example will reduce the expected life. I would be most worried about the DC bus capacitors, as they usually have a life expectancy in the thousands of hours at a particular ripple current and temperature. Higher load on the inverter means higher temperature and higher ripple current in the DC bus caps. For cheap caps the life expectancy at the rated ripple current and temperature (probably 85°C for cheap caps) could be as low as 2000 hours with a doubling of life expectancy for each 10°C below the rated temperature, so temperature plays a huge role.

Link to comment
Share on other sites

1 hour ago, Stanley said:

DC bus capacitors

Indeed. Now go and watch Easily_Bored_Engineer's videos on what kind of capacitors you might expect in this product... 🙂

To be fair... the manufacturer did update some of the components in later models, but only in terms of voltage (80V ito 63V). Life is still 2000 hours at 105 °C.

Cooked electrolytic caps remain one of my bugbears.

Edit: Rule of thumb is life doubles for every 10°C cooler, so those caps have a life of maybe 20 Phalaborwa summers 😛

 

Edited by plonkster
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...