2 minutes ago, FixAMess said:

@plonkster, thank you...

I'm totally guessing! But it looks (from the photo of the PC board with his thumb on the neutral) as if that terminal is connected to the neutral to the left of it, so that if you merely connect an earth to it, it should apply the bonding we're looking for. @Weasel just needs to confirm.

You could probably test it quite easily, doing a few voltage measurements to confirm that it is connected to neutral when running islanded, and  disconnected otherwise.

1 hour ago, plonkster said:

You could probably test it quite easily, doing a few voltage measurements to confirm that it is connected to neutral when running islanded, and  disconnected otherwise.

This would be interesting, because I remember reading that Goodwe themselves recommended to create a fixed bond?

2 minutes ago, jykenmynie said:

This would be interesting, because I remember reading that Goodwe themselves recommended to create a fixed bond?

Well, that was a recommendation for Australia... maybe over there a permanent bond is preferable over a switched one.

2 hours ago, plonkster said:

That's like... seriously.... should be in the manual or something 🙂

yes youd think so 🙃 hehe

2 hours ago, plonkster said:

Would also be interesting to see if all of them has that.

all of them i've seen yes

51 minutes ago, jykenmynie said:

This would be interesting, because I remember reading that Goodwe themselves recommended to create a fixed bond?

different countries handle it well differently. some would have to connect this through to an isolated earth spike and the backups earth should then be isolated from mains earth and only go to a spike. Not here though we bond all the earths. They try to accommodate all the options but the recommendation would have been based on region.

To connect you would typically use a 3 core in and a 3 core out. you should connect all 6, i.e. L N E backup left and L N E Grid right. you can then bond the two earths permanently in the DB or in the little connection housing underneath, Bridge PE to backup earth.  Importantly if you don't use the backup earth terminal on the inverter it wont bond the neutral when the grid fails.

I can confirm this is the way it works. if you don't connect it neutral  hovers at half of ac depending. if you do its millivolts.

 

Hi @Weasel - could you please indicate on the diagram the relay which bonds the neutral earth when inverter goes into is landing mode?

Edited by Halcyon

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.