Causes of heating at breaker junction coming from PV Strings


Veejay
 Share

Recommended Posts

dear all 

Can anyone advise - on how strings should be wired to prevent heating at high amperage output.

Insight of the problem

i have 3 strings of 4 x 350w panels - wired as follows : each string comprise of 2 panels in series then another 2 in series and then paralleled to form a string using 6mm solar cable wire 

each string is approx 18 amps Imp and 80v  Vmp. 

All 3 strings are wired separately with a positive and a neg all wired to a DB -  connected to a  25 amp fuse and then to a 25 amp breaker. with 10mm normal electrical wire 

then all 3 negatives (18 amps each ) are lopped in parallel to a 63 amp fuse and a 63 amp main breaker and then fed to the Apert 5kw inverter with 16mm electrical wire.

the same is for the positive wiring.  

i noticed heating of the wires at the breaker fuse junction and to the one closest to the main 63 amp breaker when there is a draw of up to 60 amps from the MPPT charge controller.  (NB : no heating coming down from the string wiring to the DB - No heating going away towards the inverter)

i am concerned of a fire , although you can touch the wires but it is quiet hot.

May i ask? should the individual strings be connected to each breaker and then to a buzz bar and then to the main 63 amp breaker or how can i resolve this issue.

please can anyone help urgently.

Thanks ,

Veejay

 

Link to comment
Share on other sites

I would hazard a guess that the problem is at the binding posts themselves (more specifically the interface between the binding post and the wires). A bus bar would probably help with that, and would be a cheap and easy way to check.

Edited by P1000
Link to comment
Share on other sites

Thanks guys, I removed, wiring at the breaker fuse junction on all and put in 16mm welding cable. All joints well tighten and did a test at 60amp dc draw from the pv seems stable, no heating noted but for safety I probably would put in Bus bar later on.

All the breakers are Gewiss dc/ac rated according to supplier, the fuses are ceramic gp grade. As I assume fuse should blow at over current rating

Thanks guys any more advice or feedback is welcome. 

Takecare, 

Vee 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...