Hi there

I am busy buying the hardware for a grid tied solar system.

I already have 2 off 5kva Axpert inverters. Looking to supply on average 30 - 40kwh per day. I do have 3 phase electricity but don't have 3 phase appliances etc. Just try to balance the loads. In fact have an emergency inverter and battery on one phase which keeps lights and some plugs on. The other 2 phases supply everything else with ease.

Questions

1) how many ah can the 2 inverters in parallel take. I am looking to get about 200ah 12v batteries. 3 or 4 parallel strings. 600 or 800ah

2) Should I rather do a bank per inverter although this will be expensive.

Notes:

A) I do have a large flat roof that can handle even 30 pv panels

B) at least 1 phase will be connected to eskom for ovens, pool with heat pump and underfloor heating if used. Looking at gas oven options. Unlikely that they used at the same time so single phase will be ok.

C) I may look at a 3rd inverter later

Link to comment
Share on other sites

47 minutes ago, FRZ0n said:

2) Should I rather do a bank per inverter although this will be expensive.

Axperts can't do that. They will shut down if the two units detect different voltages. Not an expert on this, that's what I heard.

Only thing that limits battery Ah is if you can charge them using the chosen inverters. Rule says charge current of 13%-15% of Ah capacity, so in theory take the combined charge capability of the two Axpert MPPTs, and you can add 5-6 times that amount of battery. :-)

Link to comment
Share on other sites

The 5Kva model is limited to 60A for Solar charging.

900ah x 13% gives you 117A. I think this is a little too high for two inverters.

I would not go this high as this does not leave much room to play with.

Depending on the size of the panels but I think for 30 you are going to be better of with 3 inverters

Link to comment
Share on other sites

I've seen 2 Axpert 5kva inverters with a battery bank of 16x 260Ah batteries, basically 1040Ah @ 48V.

Just remember, if you are going solar, you'll need enough panels to charge the bank

I know. 10 or 12 panels per inverter. 250 or 300w

Link to comment
Share on other sites

The 5Kva model is limited to 60A for Solar charging.

900ah x 13% gives you 117A. I think this is a little too high for two inverters.

I would not go this high as this does not leave much room to play with.

Depending on the size of the panels but I think for 30 you are going to be better of with 3 inverters

I have 2 inverters now. And may upgrade to a 3rd later.

Currently preparing my battery purchase. But want to buy the max allowable for the inverters.

Would be great if I can use 16 batteries as mentioned earlier. (Sorry for not crediting poster. On phone)

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...