dear friends, may you please assist me on this one.

i have 3x 8kVA Quattro inverters, all to be connected in a 3 phase set up.I have my AC in  from a 3 separate double pole 63A into individual 3 quattros.,CCGX powered up,pylontech US2000 connected.

VE Bus cables connected from the first quattro-2nd quattro ,3rd quattro the into the CCGX, I have set same values (charge current,float,absorption etc for each quattro).

the errors i am getting on the CCGX  #3, #10,#17 can someone give me light to solve this? This is my first 3phase victron installation.

 

Link to post
Share on other sites
1 hour ago, Asto said:

i have 3x 8kVA Quattro inverters, all to be connected in a 3 phase set up.I have my AC in  from a 3 separate double pole 63A into individual 3 quattros.,CCGX powered up,pylontech US2000 connected.

VE Bus cables connected from the first quattro-2nd quattro ,3rd quattro the into the CCGX, I have set same values (charge current,float,absorption etc for each quattro).

the errors i am getting on the CCGX  #3, #10,#17 can someone give me light to solve this? This is my first 3phase victron installation.

Have you configured the Quattros as a three fase system using the MK3 cable? If not, you need to go back to step one and conficure the units for a 3 phase system, only after doing that, you can configure the other settings like voltage ext..

Link to post
Share on other sites
2 hours ago, Asto said:

the errors i am getting on the CCGX  #3, #10,#17 can someone give me light to solve this? This is my first 3phase victron installation.

3-phase setups are for experienced people. Though I suppose that has the same issue as getting your first job: You need experience in order to get the job which you need to get the experience 🙂

Best I can do is point you to this document, which documents all the possible errors. #10 can be ignored (it hangs around with the others) and #3 and #17 are both saying the master/slave situation is unhealthy.

So what Jaco says is right. Go back and reconfigure using vebus quick configure. If necessary, reset each unit to factory first. Follow the instructions here.

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...