I have been using solar for about 6 years. Started with 1 Axpert 5 kw inverter and 8 BenQ 330 w panels. My Axpert got a surge and i replaced it with 2 Mecer 5 kw inverters and added 14 CNBN 330 w panels. But i could not use my BenQ panels. So i got rid of my 2 Mecer inverters and brought 3 Victron Multi 3000/48 inverters in parrellel . Running 15 CNBN on a 250/100 charge controller and my 8 BenQ on a 150/60 charge controller. I did the complete install my self.

IMG_20200709_072538.jpg

Link to post
Share on other sites
40 minutes ago, Quat Shams Allah said:

your slave is on top

You sure? I seem to recall the battery with the open top link port is the master, ie the top?

Edit: Oh hang on, I'm looking at the wrong picture. The "console" plugged tipped me off... ๐Ÿ™‚

I would move the master to the top (American politics be damned, that just seems right), and there is enough slack in the red battery cable to move that to the top module as well (so you get proper cross-link cancelling out of cable resistance).

Edited by plonkster
Link to post
Share on other sites
1 minute ago, plonkster said:

You sure? I seem to recall the battery with the open top link port is the master, ie the top?

Yeah but it looks a bit funny, because his Lan Port 0 is open (how Pylontech defines the master)ย on the top battery but the CAN port on the bottom battery is being used, I seem to recall the Pylontech manual says you need to run the CAN cable from the master also.

@vulgrim, do you pick up the batteries correctly in your "devices" list when you open up your Venus' control panel?

Link to post
Share on other sites
6 minutes ago, jykenmynie said:

Yeah but it looks a bit funny, because his Lan Port 0 is open (how Pylontech defines the master)ย on the top battery but the CAN port on the bottom battery is being used, I seem to recall the Pylontech manual says you need to run the CAN cable from the master also.

I got confused between @Quat Shams Allah's photo and the original. He added a pic of his own install as an example. The example is of course correct (along with that console cable cause it's likely an ICC-managed thing).

@vulgrim has his master at the bottom, so the CAN-cable is in the right spot (for now, it may have to move with the suggested reconfiguration). The issue is that the cables going from the battery to the rest of the system isn't cross-connected, they are both connected to the bottom battery. That of course needs to be improved (and the easiest is to move the red cable up, it has enough slack). I'm not sure about the requirement that the negative has to be on the last slave, but I will not dispute that. It is possible that the way the battery takes voltage measurements needs it to be that way (ideally) so that the lowest possible point (in terms of voltage) is at the last slave, and the highest possible voltage is on the positive side of the master. Those little links, after all, have tiny bits of resistance in them and technically form a large voltage divider chain ๐Ÿ™‚

Edited by plonkster
Link to post
Share on other sites
1 minute ago, plonkster said:

I got confused between @Quat Shams Allah's photo and the original. He added a pic of his own install as an example. The example is of course correct (along with that console cable cause it's likely an ICC-managed thing).

@vulgrim has his master at the bottom, so the CAN-cable is in the right spot. The issue is that the cables going from the battery to the rest of the system isn't cross-connected, they are both connected to the bottom battery. That of course needs to be improved (and the easiest is to move the red cable up, it has enough slack). I'm not sure about the requirement that the negative has to be on the last slave, but I will not dispute that. It is possible that the way the battery takes voltage measurements needs it to be that way (ideally) so that the lowest possible point (in terms of voltage) is at the last slave, and the highest possible voltage is on the positive side of the master. Those little links, after all, have tiny bits of resistance in them and technically form a large voltage divider chain ๐Ÿ™‚

I don't think it is a requirement, per say, but it was explained to me that it just helps the charging/discharging of the stack to be ever so slightly more "balanced". Guess it can't hurt to do it!

Link to post
Share on other sites
5 minutes ago, jykenmynie said:

slightly more "balanced".

Those PN balancers can only shuffle 50mA across, which would under heavy discharge possibly be insufficient. It's easy to get it right (those cables just clip on and off) ๐Ÿ™‚

ย 

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

ร—
ร—
  • Create New...