Irrisol Posted July 10, 2020 Share Posted July 10, 2020 Hi all, Installed a solis 4g Grid tied system, and CT keeps giving Range error. Checked ratio and it is set correctly. Customer has a rural supply on prepaid, with the control panel of meter that plugs into wall outlet, and uses PLC (power line communication) to communicate with meter unit at eskom supply point. My question is, if I was to re-wire a plug, so that this meter could be plugged in between CT and Grid, would this resolve the issue. Also customers DB board is a mess of wires, could this create interference with the CT clamp. I have never had this issue and am stumped Quote Link to comment Share on other sites More sharing options...
Jaco De Jongh Posted July 10, 2020 Share Posted July 10, 2020 2 hours ago, Irrisol said: My question is, if I was to re-wire a plug, so that this meter could be plugged in between CT and Grid, would this resolve the issue. This should not have an effect at all. 2 hours ago, Irrisol said: Also customers DB board is a mess of wires, could this create interference with the CT clamp. Neither should this make any difference. To me it sounds like a setting issue. Quote Link to comment Share on other sites More sharing options...