David Botha Posted September 15, 2020 Posted September 15, 2020 I have 4 Canadian 320w panels connected. They are divided into 2 strings of 2 panels each and then connected in parallel with y-MC4 connectors. The Voc of each panel is 45v and their Imp 8amp. Am I correct in calculating their combined volts as 90 and their amps as 16? Is the 30amp of the fuse in the combiner box high enough for their current? Quote
Jay-Dee Posted September 15, 2020 Posted September 15, 2020 You are correct re the 90v / 16A... Not knowing the model, just check the MAX / PEAK current ratings re the fuse... Rather blow fuses than panels.. If your panels are peaking at 8 amp, I would personally go lower than 30A as that is almost double the peak rating. I would sooner look at around a 20A Quote
David Botha Posted September 15, 2020 Author Posted September 15, 2020 Thanks Jay-Dee. The fuse is a Bussmann ETN Series 1000V dc 30 amp. How can I check the MAX / Peak current? Quote
Jay-Dee Posted September 16, 2020 Posted September 16, 2020 You need to confirm the model of your panels and then find the data sheet online In my case, I have the CS3U-355P panels https://sicessolar.com.br/wp-content/uploads/2017/12/CSI_KuMax_CS3U-345-360-P.pdf As per the data sheet, they have a short circuit AMP rating of 9.67A per panel. In a 2S2P config this would mean that the fuse should ideally be 20A and not higher (to be effective) I would presume a 20A be the best fit for yours too as I doubt you will get an 18A anywhere Quote