1 hour ago, MartinKoch said:

1x 3.5 and 2x 2.4 pylontech lythium batteries, current setting is 30A, was the setting with only the 2x 2.4 batteries, does it needs to change with the added 3.5 kwh? 

For 2 x 2.4 it should have been 50A (25A for each 2.4)

Now that you've added 3.5 Must be 80A (37A for each 3.5) Not 90A

Edited by Quwatush Shams (Suly)
Link to post
Share on other sites
20 minutes ago, MartinKoch said:

Thank you, I can only select 20A or 30A, thus either 60 or 90 combined, will 60A be better? 

The inverter setting is total charging current, not per battery.  So, you should set 80A - it will be divided by the BMS between the batteries.

Link to post
Share on other sites
1 hour ago, MartinKoch said:

Did set to 80A, very little knowledge of this issue, what is the benefit of correct setting VS for instance 30A? Quicker charging time, battery performing more optimally or what? 

The 80A is essentially the maximum recommended value.  If your batteries will charge fully at a lower setting, by all means use it.

Generally, lower current is better as the power wasted (because of the internal resistance of the battery) goes up with the square of the current.  This wasted power also heats the batteries, which is not a good thing.

 

Link to post
Share on other sites
4 hours ago, MartinKoch said:

what is the benefit of correct setting VS for instance 30A? Quicker charging time,

Yes. Quicker charging time is the main benefit. But it may also prolong battery life, as the battery can use more solar power (if and when available), so it doesn't spend so much time at very low states of charge (low SOC); low SOC is bad for nearly all battery types.

Also, the Axpert chargers use the value in setting 02 to determine the end of charge condition. With factory firmware, it's 1/5th of the value in the setting. If you leave this value too low, the termination condition will be very low (though the inverter has a minimum value for this, 5 A comes to mind).

Link to post
Share on other sites
1 hour ago, MartinKoch said:

indicating 28 on battery temperature, that stlii low enough? Referring to Calvin's feedback 

I think that 28°C is fine for the battery modules. Unless your total battery capacity is quite small relative to your needs, I don't think that the life improvement from charging slower would be significant.

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...