15 minutes ago, Chris Hobson said:

Unfortunately - 10 points for Voltronic (or their affiliates) for not supplying the manual. TTT will be rolling his eyes.

On the contrary, I am quite pleased that you are being fair in not only penalizing Victron, but Voltronics also. :D

Link to comment
Share on other sites

2 hours ago, The Terrible Triplett said:

On the contrary, I am quite pleased that you are being fair in not only penalizing Victron, but Voltronics also. :D

Equal opportunity critics... love them too :-)

Link to comment
Share on other sites

  • 3 years later...
1 hour ago, Fazil said:

would this logic apply to the Infini solar 10kw in parallel?

Error 60

Generally, the Axpert and Infini fault codes (error codes) don't seem to line up.

However, in this case, it appears that they do (from a different model's manual, but should still apply):

755869190_Faultcode60.png.29237323b2002a5d40e45a222f7c9e12.png

Link to comment
Share on other sites

  • 3 weeks later...

Good day all

I have 2 x 5kva Axperts connected in parallel with similar issue all was 100% until after installing rasPi and icc (no wiring changes) now have error code 60, have noticed now master goes into bypass which has grid voltage output at 237v and slave still in inverter mode at 230v output which is obviously causing the current feedback issue, any help from the axpert fundis would be greatly appreciated.

Link to comment
Share on other sites

@Rob Firefly, I would check setting 28 (output mode) and make sure that individually these are set to Par. If you need to change one of them, note that you have to have the inverter switched off to do it. Have a charge source available (PV or AC-in) so the inverter doesn't actually switch off completely.

I would disconnect both inverter's AC-out (hopefully you have a circuit breaker on each) until you sort this out. There should be safeguards, but I worry about loud bangs when the outputs aren't singing from the same song book, so to speak.

Link to comment
Share on other sites

It's possible that the current sharing cable connections work loose; that's been reported before. I suppose the parallel card could have failed, but I would have expected an error to be detected (to do with CAN bus errors). 

Link to comment
Share on other sites

  • 1 year later...
6 hours ago, Rodney said:

I'm picking up a error code 60 when ac power is reinstated from the grid.

This fault comes up when significant power (like 1200 W) is detected flowing into the inverter output. This seems to be possible with paralleled inverters, if the current sharing isn't working.

* Do you have paralleled inverters?

* If you have one inverter, is setting 28 set to PAL? The easiest way is to check whether you see "HS" in the display, indicating that it's a parallel master. If so, you need to turn it off; see FAQ question 4.

Link to comment
Share on other sites

16 hours ago, Coulomb said:

This fault comes up when significant power (like 1200 W) is detected flowing into the inverter output. This seems to be possible with paralleled inverters, if the current sharing isn't working.

* Do you have paralleled inverters?

* If you have one inverter, is setting 28 set to PAL? The easiest way is to check whether you see "HS" in the display, indicating that it's a parallel master. If so, you need to turn it off; see FAQ question 4.

Thank you , I will go to my client in the morning.

Link to comment
Share on other sites

  • 1 year later...
On 2020/07/12 at 2:00 PM, Coulomb said:

This fault comes up when significant power (like 1200 W) is detected flowing into the inverter output. This seems to be possible with paralleled inverters, if the current sharing isn't working.

* Do you have paralleled inverters?

* If you have one inverter, is setting 28 set to PAL? The easiest way is to check whether you see "HS" in the display, indicating that it's a parallel master. If so, you need to turn it off; see FAQ question 4.

I dont know how to say this you are amazing and you are a god sent, it's me I just installed a new 5000w mercer and followed your instructions and voila done,  both up and running, it takes about 45 seconds to die after turning off the switch.

 

Thank you, let me know if I can be of assistance....

Thanks greatly appreciated...

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...