I have the following system installed:

Schneider XW+7048 Inverter

 

Charge Controller MPPT 60 150

 

12 * 310w Renesola Solar panels 

 

24 * Willard RT17 560ah flooded 2V batteries

 

SCP 

 

 

I require anyone with Schneider expertise that can check my installation, I want to make sure everything is done correctly. (Off course I will pay)

Pretoria East area

 

IMG_0013.jpg

IMG_0071.jpg

Link to comment
Share on other sites

That chimney is going to give you partial shading at some point in time.  Why was the panels not moved higher up the roof and those two next to the flat panel moved somewhere else? I'm not familiar with your inverter, but I assume one serial string of panels - if only one cell of one panel is in the shade it effects the total PV generation.

Link to comment
Share on other sites

  • 4 weeks later...

My inverter is still using some power from the grid even when the batteries are fully charged.  It's a 7kw inverter and my usage will be 3kw then it will draw 800w from the grid. I have set Load Shaving On at 0A and Sell to grid on at 0A etc etc on the Schneider but still.   

Link to comment
Share on other sites

How do you measure the 800w? Could be just a really bad power factor.

I must get that electricity meter thing of mine onto the play store. It's an app that uses the phone camera to count flashes on the prepaid meter led and tell you your power use.

Sent from my GT-I9195 using Tapatalk

Link to comment
Share on other sites

The Schneider Inverter has a Control Panel which shows total load and power imported or exported to the Grid. Attached also a graph of elec usage of Yesterday from the Tshwane Prepaid Smart meter.My monthly usage is still about 270 units which is about 50% of my total usage.

Yesterdays consumption.JPG

Monthly Summary.JPG

Link to comment
Share on other sites

  • 3 weeks later...

Hi lancelot,

Your charge controller is slightly undersized. The datasheet for the MPPT 60 150 states the max output power is 3500W, but this is at 60V. The limiting factor is the current output of 60A which means 2880W at 48V.

The XW+ will always draw some current from the grid if sell is disabled. Also the load shaving function will only draw down the battery voltage to the value of Grid Supp Volts setting.and will switch off completely at V= Recharge +0.5V. Have you tried enabling Enhanced Grid Support mode instead of load shave?

Link to comment
Share on other sites

  • 6 years later...

Hi Lancelot,

Just stumbled on this post.

Did you manage to get a true Schiender installer who understands this system?

i had my system installed awhile back, however i have the same issues. I have two 60/150 MPPT, with a 5.5Kw solar panel capacity.

I seem to max out at 3200w daily generation irrespective of the sun being high and also have the system constantly drawing from the grid.

Thanks.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...