Charging batteries from Grid


Brian Chetty
 Share

Recommended Posts

I have 1 x 4.8kwh 100amp h battery ..it was fully charged by solar.

Bulkcharge voltage set to 56.4v

Floating charge voltage set to 54v

Low DC cut off voltage set to 42v

Overload bypass is enabled. 

I was expecting it to use battery solar and first..

But I realised that it's set to go to line mode if the overload in battery is detected.  But just wondering is the battery can deliver 5kva for at lease a short while before inverter switches to grid?

Link to comment
Share on other sites

20 hours ago, Brian Chetty said:

But just wondering is the battery can deliver 5kva for at lease a short while before inverter switches to grid?

Ordinary lead acid batteries don't like heavy discharges; 5 kW would be over 100 A, so over 5C for a 100 Ah battery. This will not be good for long life.

They would probably provide that power for a few minutes, at the expense of battery life, if the inverter allowed it to (e.g. if there was no AC-in). But likely the battery voltage would sag so much that the inverter-charger (especially without the KettleKomp™ feature of patched firmware) would immediately switch to grid.

200 Ah (of nominally 48 V) is the minimum recommended size for a 5 kVA (especially a 5 kW) inverter.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...