Roche Smith Posted October 24, 2020 Share Posted October 24, 2020 can I use a 3kw Mecer solar inverter to power up a .55kw submersible borehole pump? The head of pump is 20m. Quote Link to comment Share on other sites More sharing options...
0 Gerrit123 Posted May 31, 2023 Share Posted May 31, 2023 I would also like to know. Has anyone used a little inverter with a borehole? Quote Link to comment Share on other sites More sharing options...
0 BritishRacingGreen Posted June 1, 2023 Share Posted June 1, 2023 10 hours ago, Gerrit123 said: I would also like to know. Has anyone used a little inverter with a borehole? @Scorp007 whats your experience or opinion in matchings such loads to 3kw inverter? Quote Link to comment Share on other sites More sharing options...
0 FixAMess Posted June 1, 2023 Share Posted June 1, 2023 Victron equipment is suited to starting inductive loads. I know of a 3kVA multi2 that is for sale, R14K, I can pass the details on if the poster is interested. Quote Link to comment Share on other sites More sharing options...
0 Scorp007 Posted June 1, 2023 Share Posted June 1, 2023 On 2020/10/24 at 4:44 PM, Roche Smith said: can I use a 3kw Mecer solar inverter to power up a .55kw submersible borehole pump? The head of pump is 20m. No problem at all. I have started 0.75kw induction motors like my caravan mover with a 1.5kw brick inverter without problems. People overplay the very short spike in current during the 1st 2 seconds. We don't all have to run to fit a VSR. MY 3kW Axpert runs great even on my 3 times larger Ryobi table saw. The key is good battery power to provide the amps in the first few seconds. Using with PV then even less of a problem. BritishRacingGreen 1 Quote Link to comment Share on other sites More sharing options...
0 Scorp007 Posted June 1, 2023 Share Posted June 1, 2023 (edited) 3 hours ago, FixAMess said: Victron equipment is suited to starting inductive loads. I know of a 3kVA multi2 that is for sale, R14K, I can pass the details on if the poster is interested. Most inverters with a 2x current peak for 10sec will start pumps. It's only when you have high enertia machine that starting becomes problematic. Compressors without unloading valves, some huge fans and equipment with flywheels etc. Edited June 1, 2023 by Scorp007 FixAMess 1 Quote Link to comment Share on other sites More sharing options...
Question
Roche Smith
can I use a 3kw Mecer solar inverter to power up a .55kw submersible borehole pump?
The head of pump is 20m.
Link to comment
Share on other sites
5 answers to this question