ianm Posted April 12, 2021 Share Posted April 12, 2021 Better explanation here: https://www.sunsynk.org/post/basic-understanding-of-the-sunsynk-inverter Jump to the 14:53 position. Yellow Measure 1 Quote Link to comment Share on other sites More sharing options...
Trev Posted April 13, 2021 Share Posted April 13, 2021 (edited) Thanks @ianm I tried finding some reference from Keith but clearly missed it. This would have helped. @Brani yes confirmed, CT connections to be in installed on 5-6. I hear you kn the level of nervousness Last night after a final check and ensuring that my earth-bond relay was engaging I switched ON. All good and running nicely as an expensive UPS for now. Looking forward to the solar installation next... Thanks to everyone for your assistance! Edited April 13, 2021 by Trev Quote Link to comment Share on other sites More sharing options...
TonyH Posted April 13, 2021 Share Posted April 13, 2021 Neat installation. Are the AC and DC separated inside the trunking by a metal trunking inside? Trev 1 Quote Link to comment Share on other sites More sharing options...
Luminous Posted April 13, 2021 Share Posted April 13, 2021 Another confusion is that the 5.5kw and the 8.8kw does not use the same markings for connecting up the GEN/GRID/LOAD. 8.8kw is GRID/GEN/LOAD 5.5kw is GEN/LOAD/GRID 8.8kw is X/N/L 5.5kw is L/N/E Trev 1 Quote Link to comment Share on other sites More sharing options...
Trev Posted April 13, 2021 Share Posted April 13, 2021 8 hours ago, TonyH said: Are the AC and DC separated inside the trunking by a metal trunking inside Thank you @TonyH, there is no mixing of AC & DC cables in the trunking. The battery cables run upwards and jump over in flex conduit. The AC cables run alone in the horizontal trunking. When I install my solar strings they will run in their own trunking. Yellow Measure and TonyH 2 Quote Link to comment Share on other sites More sharing options...
Imran R Posted April 25, 2021 Share Posted April 25, 2021 Hi guys I’ve just picked up an issue this evening where my prepaid input meter does not connect to the main box on the street whilst the inverter is working. When I switch off the inverter and connect directly to the grid, the prepaid meter connects with no issues. This has never happened before as I have my inverter system for a couple of months now. Anyone else experienced a similar issue or know what the problem could be? Thanks Quote Link to comment Share on other sites More sharing options...
Leshen Posted April 26, 2021 Author Share Posted April 26, 2021 5 hours ago, Imran R said: Hi guys I’ve just picked up an issue this evening where my prepaid input meter does not connect to the main box on the street whilst the inverter is working. When I switch off the inverter and connect directly to the grid, the prepaid meter connects with no issues. This has never happened before as I have my inverter system for a couple of months now. Anyone else experienced a similar issue or know what the problem could be? Thanks Hi Imraan. We did a few installs where the prepaid meter that plugs in to recharge doesnt work on the load side of the inverter. Once connected to the grid side, it works fine so we merely do a permanent install into the grid side of the inverter. Yellow Measure 1 Quote Link to comment Share on other sites More sharing options...
Imran R Posted April 26, 2021 Share Posted April 26, 2021 Hi Leshen Thanks for the reply. That would make sense. How does one actually go about doing this? Quote Link to comment Share on other sites More sharing options...
Luminous Posted April 26, 2021 Share Posted April 26, 2021 I was afraid of the same happening to me, so what I did was where my inverter was installed in the garage I added another grid circuit. This was taken before the inverter. As all my circuits are on the essential loads except this one. This will then be used to power heavy loads like my welding machine or something that will be to much for the inverter. And if I had a problem with the power meter I can just plug it in there. Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted April 26, 2021 Share Posted April 26, 2021 1 hour ago, Imran R said: Hi Leshen Thanks for the reply. That would make sense. How does one actually go about doing this? Quote Link to comment Share on other sites More sharing options...
Imran R Posted April 26, 2021 Share Posted April 26, 2021 @ luminous & @ yellowtapemeasure, thanks for the clarity. Will have a look at my DB tomorrow to see how I can connect the unit. Hopefully it will be easy. 17 hours ago, leshen said: Hi Imraan. We did a few installs where the prepaid meter that plugs in to recharge doesnt work on the load side of the inverter. Once connected to the grid side, it works fine so we merely do a permanent install into the grid side of the inverter. Yellow Measure 1 Quote Link to comment Share on other sites More sharing options...
Imran R Posted April 26, 2021 Share Posted April 26, 2021 17 hours ago, leshen said: Hi Imraan. We did a few installs where the prepaid meter that plugs in to recharge doesnt work on the load side of the inverter. Once connected to the grid side, it works fine so we merely do a permanent install into the grid side of the inverter. Hi Leshen Where are you based? Is there a way I can contact you? Quote Link to comment Share on other sites More sharing options...
Leshen Posted May 12, 2021 Author Share Posted May 12, 2021 Hi guys. Extract from Global Tech The warranty period of the products will depend on its type and the accreditation of the installer. Not sure how many of the end users installed it themselves. Quote Link to comment Share on other sites More sharing options...
Leshen Posted May 12, 2021 Author Share Posted May 12, 2021 44 minutes ago, Vassen said: This accreditation only came along recently. I was told that I could install it and as long as an electrician signs it off, it will be fine. Their accreditation system is anyway flawed to a certain extent as it only looks at the number of installs one has done. I’ve already done 2, need 3 more installs to get accredited unless the requirements have changed. Will get more info from Global Tech on their warranty requirements. Quote Link to comment Share on other sites More sharing options...
Tariq Posted May 12, 2021 Share Posted May 12, 2021 (edited) @Vassen, you did mine and I did yours i got mine from Ellies, they have a 4 page form that has to be filled out, lot of questions regarding the installation and also, if signed off by an electrician than it is covered by warranty. I seem to know a lot more than my CERTIFIED electrician friend, and I am only a DIY guy Edited May 12, 2021 by Tariq Yellow Measure 1 Quote Link to comment Share on other sites More sharing options...
JV0_11_ Posted May 23, 2021 Share Posted May 23, 2021 On 2021/04/25 at 10:21 PM, Imran R said: Hi guys I’ve just picked up an issue this evening where my prepaid input meter does not connect to the main box on the street whilst the inverter is working. When I switch off the inverter and connect directly to the grid, the prepaid meter connects with no issues. This has never happened before as I have my inverter system for a couple of months now. Anyone else experienced a similar issue or know what the problem could be? Thanks That will cause you issues, like for me - power produced by solar or batteries was being subtracted from my units. To solve this, i left the garage plugs on the grip( only plus in the whole house) and plugged the meter there. Quote Link to comment Share on other sites More sharing options...
Imran R Posted May 24, 2021 Share Posted May 24, 2021 Hi there It’s not possible that the energy generated would be subtracted from your units as you mentioned unless you were feeding back into the grid, but then again your meter will be running in the opposite direction. Maybe you might have some other equipment that is drawing power. Just to indicate that I’ve managed to sort out the issue though Leshen’s assistance who is on this forum as well. I must say that Leshen and his team went out of their way to ensure that not only the original problem was resolved but also suggested a minor improvement on my system which was done as well. My prepaid unit was installed on the Eskom side before the inverter to ensure communication with the main electrical box on the outside of the house as opposed to previously having the unit plugged into one of the plugs in the house which is fed from the inverter which therefore caused communication errors. It’s been just over two weeks now and no issues so far. Perhaps one of the guys on here can assist you further with your issue. Yellow Measure and Leshen 1 1 Quote Link to comment Share on other sites More sharing options...
Schallas Posted June 25, 2021 Share Posted June 25, 2021 On 2021/04/25 at 10:21 PM, Imran R said: Hi guys I’ve just picked up an issue this evening where my prepaid input meter does not connect to the main box on the street whilst the inverter is working. When I switch off the inverter and connect directly to the grid, the prepaid meter connects with no issues. This has never happened before as I have my inverter system for a couple of months now. Anyone else experienced a similar issue or know what the problem could be? Thanks I had the same issue... Turns out, and this is what the Tshwane Electrician told me, was that the electricity from the inverter, and the electricity from Eskom will have a phase difference, and that causes the meter give the errors. I installed a "on grid" plug in the garage which sorted out the issue... Its also handy if you have large tools that you like to run, which then doesn't have to start up on you inverter/panels/battery Yellow Measure 1 Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted June 26, 2021 Share Posted June 26, 2021 13 hours ago, Schallas said: I had the same issue... Turns out, and this is what the Tshwane Electrician told me, was that the electricity from the inverter, and the electricity from Eskom will have a phase difference, and that causes the meter give the errors. I installed a "on grid" plug in the garage which sorted out the issue... Its also handy if you have large tools that you like to run, which then doesn't have to start up on you inverter/panels/battery If there really was a phase difference, with a hybrid / on-grid inverter, then there would be a big BOOM!. The issue is around the PLC that these CIUs use to communicate with the meter in the street. In my own experience it is usually very iffy, even without an inverter in the way (which messes it up completely). Installing a dedicated plug socket for it on the grid side, like you have done, is the only long-term solution. Quote Link to comment Share on other sites More sharing options...
Imran R Posted August 15, 2021 Share Posted August 15, 2021 Hi guys. Just picked up an issue regarding my BSL 6.4kw battery which is connected to the 8kw Sunsynk inverter. For the second time within a month, the battery completely depleted to 0%. It then recharged and continued to work normally. My setting for the battery to shut down is 20%. Have any of you experienced such an issue before or know what the issue could be? Thanks Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted August 16, 2021 Share Posted August 16, 2021 22 hours ago, Imran R said: Hi guys. Just picked up an issue regarding my BSL 6.4kw battery which is connected to the 8kw Sunsynk inverter. For the second time within a month, the battery completely depleted to 0%. It then recharged and continued to work normally. My setting for the battery to shut down is 20%. Have any of you experienced such an issue before or know what the issue could be? Thanks Either bad comms between BMS and inverter (cable?), or the BMS may need a firmware upgrade (assuming that your Sunsynk's firmware is also up to date). Quote Link to comment Share on other sites More sharing options...
Imran R Posted August 16, 2021 Share Posted August 16, 2021 I’ve checked the cables and they look fine. I’ve got the latest software on the inverter. I’m assuming that only the supplier can do the firmware upgrade for the BSL battery? Quote Link to comment Share on other sites More sharing options...
EugeneN Posted August 16, 2021 Share Posted August 16, 2021 Hi everyone. Need some help setting my 2 day old 8kw Synsynk inverter. I need to know what I must set the charge/discharge rate for my batts at. I have 2 x 3.5kw Pylontech batts with specs: 48v, 74Amp and a 0.5C rate. That means the continues current is 37A per batt. The installer set my rate to 37A and Im pretty sure it should be 74A (37A cont current x 2batts). With that, I also think Batt capacity should therefor be 148Ah and not 74Ah. Any thoughts? Quote Link to comment Share on other sites More sharing options...
Yellow Measure Posted August 16, 2021 Share Posted August 16, 2021 6 hours ago, Imran R said: I’ve checked the cables and they look fine. I’ve got the latest software on the inverter. I’m assuming that only the supplier can do the firmware upgrade for the BSL battery? Yes, I remember reading something about that, give them a call and find out? Quote Link to comment Share on other sites More sharing options...
Leshen Posted August 16, 2021 Author Share Posted August 16, 2021 40 minutes ago, EugeneN said: Hi everyone. Need some help setting my 2 day old 8kw Synsynk inverter. I need to know what I must set the charge/discharge rate for my batts at. I have 2 x 3.5kw Pylontech batts with specs: 48v, 74Amp and a 0.5C rate. That means the continues current is 37A per batt. The installer set my rate to 37A and Im pretty sure it should be 74A (37A cont current x 2batts). With that, I also think Batt capacity should therefor be 148Ah and not 74Ah. Any thoughts? Hi. You are correct. Battery capacity is 148AH and charge and discharge amps should be 74A EugeneN and Yellow Measure 1 1 Quote Link to comment Share on other sites More sharing options...