Raj35 Posted January 14, 2021 Posted January 14, 2021 Hi Everyone needs some advice I'm adding solar panel to my system Axpert King Inverter 5kva. I'm adding 10 x JA 390 watt panels or Jinko 405watts ,please if anyone used these panel which is better suited. Connection will be 2S3P and 2S2P. 6mm2 cable to combiner box one 40amp and one 16amp breaker with fuse and 10mm2 cable from combiner to inverter. 6mm2 has a run of +- 15meters and 10mm2 under 5 meter. Your advice with be appreciated thanks. Quote
Dani Posted January 14, 2021 Posted January 14, 2021 3 hours ago, Nirvaan said: Connection will be 2S3P and 2S2P. Don't think this will work. How many Mppts do you have? What's the pv voltage range? If it's the normal 145vdc then you need sets of 2 to get the voltage right. Quote
Coulomb Posted January 15, 2021 Posted January 15, 2021 10 hours ago, Dani said: If it's the normal 145vdc then you need sets of 2 to get the voltage right. 2S3P and 2S2P are both two panels in series, which should be right. 16A sounds a bit light for 2P of large panels. What is the Imp of the panels? Quote
Raj35 Posted January 15, 2021 Author Posted January 15, 2021 11 hours ago, Dani said: Don't think this will work. How many Mppts do you have? What's the pv voltage range? If it's the normal 145vdc then you need sets of 2 to get the voltage right. @ Dani 1Mppt max volts 145Pv array. Operating volts 60 to 115V. PV volts 40volts Voc 49.5Volts. One string 80Volts 30amp the other 80Volts 20amp. Quote
Raj35 Posted January 15, 2021 Author Posted January 15, 2021 52 minutes ago, Coulomb said: 2S3P and 2S2P are both two panels in series, which should be right. 16A sounds a bit light for 2P of large panels. What is the Imp of the panels? @Coulomb my apologies it should be 20amps. Imp is 9.70volts.One string will be 80Volts 30amp and thee other 80Volts 20amp parallel = 3900 watts 80Volts 50amp with a main MCB of 63amp in combiner box to inverter. Quote
Raj35 Posted January 15, 2021 Author Posted January 15, 2021 JAM72S09_PR_375-395_Global_EN_20190515A.pdf Quote
Coulomb Posted January 15, 2021 Posted January 15, 2021 2 hours ago, Nirvaan said: my apologies it should be 20amps. Ok, but the Imp is very close to 10 A at 25°C. At higher temperatures, it will be slightly higher. (Less power because the voltage drops by a larger amount, but the breaker only cares about current.) You may find yourself with nuisance trips of the 20 A breaker. I'm amazed that they can get 395 W out of 72-cell panels these days. I thought they might have gone to 78 (13 x 6) or more cells. Quote
Raj35 Posted January 15, 2021 Author Posted January 15, 2021 4 hours ago, Coulomb said: Ok, but the Imp is very close to 10 A at 25°C. At higher temperatures, it will be slightly higher. (Less power because the voltage drops by a larger amount, but the breaker only cares about current.) You may find yourself with nuisance trips of the 20 A breaker. I'm amazed that they can get 395 W out of 72-cell panels these days. I thought they might have gone to 78 (13 x 6) or more cells. @Coulomb thanks I will change to 25amp.Will 32amp be an over kill.I have attached a Jinko panel specs.Which are better panels or do you of goods ones thanks. CheetahPerc JKM390-410M-72H-(V)-A3-EN.pdf Quote
Coulomb Posted January 16, 2021 Posted January 16, 2021 13 hours ago, Nirvaan said: Will 32amp be an over kill. Yes, 25 A will be safer. Quote Which are better panels or do you of goods ones thanks. Sorry, I know nothing of modern panel quality etc. Quote
Raj35 Posted January 16, 2021 Author Posted January 16, 2021 4 hours ago, Coulomb said: Yes, 25 A will be safer. Sorry, I know nothing of modern panel quality etc. @Coulomb thanks for the advice. Quote