PickleRick Posted January 23, 2021 Posted January 23, 2021 I have 12 x 370W panels split into 4 strings (3 panels per string) Supplying ~120V and 3700W peak to my inverter. My desired scenario is to carry all loads on the panels during clear sky daytime. Today was such a day, but as soon as I introduce a total load of over 1000W (pool + appliances), Solar Usage drastically drops and power is thus provided from the battery & panels <- undesired. I believe my panels have sufficient power to carry all loads, but sadly the inverter does not allow it. The battery manual recommends configuring these settings if not connected via BMS, which I am not. My current Settings are as follows - and have played with the SBU setting, but still no joy.. 1. SOL 2. 50A 5. USE 11. 30A 12. 47.7V 13. 51.5V 14. OSO 19. 55V 20. 55V 21. 44V 22. SBd Any assistance will be appreciated. Quote
hoohloc Posted January 23, 2021 Posted January 23, 2021 2 hours ago, PickleRick said: I have 12 x 370W panels split into 4 strings (3 panels per string) Supplying ~120V and 3700W peak to my inverter. My desired scenario is to carry all loads on the panels during clear sky daytime. Today was such a day, but as soon as I introduce a total load of over 1000W (pool + appliances), Solar Usage drastically drops and power is thus provided from the battery & panels <- undesired. I believe my panels have sufficient power to carry all loads, but sadly the inverter does not allow it. The battery manual recommends configuring these settings if not connected via BMS, which I am not. My current Settings are as follows - and have played with the SBU setting, but still no joy.. 1. SOL 2. 50A 5. USE 11. 30A 12. 47.7V 13. 51.5V 14. OSO 19. 55V 20. 55V 21. 44V 22. SBd Any assistance will be appreciated. Hi, your string voltage is higher than what it should be. Max is 115Vdc, so you need to connect your PV panels in two series, six parallel strings. Check Page 11 of the installation manual. Start there and see how it goes Quote
PickleRick Posted February 11, 2021 Author Posted February 11, 2021 Hi Thanks hoohloc. I changed my setup to 2P2S with an average voltage of 80V to the inverter. Sadly, my problem still persists. As soon as the battery is full, the inverter would rather drain from the battery or use eskom, when I have a full "Sun Day". Quote
jan793 Posted April 6, 2021 Posted April 6, 2021 Try changing setting 22 to SbE, "Max input solar power = Max battery charging power + Connected load power" Quote
Alex Feldmann Posted April 7, 2021 Posted April 7, 2021 Assume Solar Module 1S Voc = 48.2V Vmp = 39.6V Imp 9.35A Solar Array 6P2S x6 Strings in parallel Vmp = 79.2 Imp = 56.1A Solar Wire Sizing Recommended Assume 40 meter between combiner box and Inverter Wire size of 16mm2 is Required for <3% Volt drop @ Imp 56.1 Wire size of 10mm2 is Required for <3% Volt drop @ Imp 45A Recommendation would be to check if a 16mm2 solar cables (Or x3 6mm2 per phase) are installed. If the solar cable is not 16mm2 (Or x3 6mm2 per phase) then the solar array cannot supply the max. required power to the inverter when the load is increased, due to power losses within the cables For additional info Refer to inverter manual page 9 PickleRick 1 Quote
Alex Feldmann Posted April 7, 2021 Posted April 7, 2021 7 minutes ago, Alex Feldmann said: Assume Solar Module 1S Voc = 48.2V Vmp = 39.6V Imp 9.35A Solar Array 6P2S x6 Strings in parallel Vmp = 79.2 Imp = 56.1A Solar Wire Sizing Recommended Assume 40 meter between combiner box and Inverter Wire size of 16mm2 is Required for <3% Volt drop @ Imp 56.1 Wire size of 10mm2 is Required for <3% Volt drop @ Imp 45A Recommendation would be to check if a 16mm2 solar cables (Or x3 6mm2 per phase) are installed. If the solar cable is not 16mm2 (Or x3 6mm2 per phase) then the solar array cannot supply the max. required power to the inverter when the load is increased, due to power losses within the cables For additional info Refer to inverter manual page 9 Change <3% to <10% PickleRick 1 Quote
PickleRick Posted April 27, 2021 Author Posted April 27, 2021 (edited) Thanks. I have 2 strings coming from the panels to the fuses. From the fuses, I'm then combining them to 1 string to the Inverter. Cables from Panels are 6mm - Cables from Fuses to Inverter are 16mm2. I cant feel any hot wires when solar input is maximum, but they are sightly on the warm side. Appreciate all the help thus far. With some tinkering and a bit more battery storage, I've managed to get to a more comfortable place. I'm nowhere near the 4200W of installed panels, But I'll take what I'm currently getting. No eskom used at all on most days. Edited April 27, 2021 by PickleRick Updated Quote