Meccer - SOL-I-AX-5D

Rated power - 5000va

DC input - 48 VDC , 117 Amps 

AC output - 230 VAC 

AC charger mode 

AC input - 230 VAC - 35 Amps 

DC output - 54 VDC 

Max 60 Amps : default 30 amps 

 

System  has been up and running for just over 2 years ( longest outage, 12 hours and the system was still operating) at the time of installation I had no research into inverter system (a newbie). I had installed made up UPS systems and backup generators.

Top Sub  DB  - 6 mm supply cable from the main DB  - supply to the inverter , 2 plug circuits and a light circuit.

Inverter DB - 4 mm cable from the inverter - 4 plug circuits - for a server, computers and screens, alarm, CCTV, and  telephone system. 

All the socket outlets fed from the inverter are blue dedicated socket outlets. 

2 compartment trunking ... top trunking has the AC power cables and the bottom trunking has the  with DC power cables (1000V 35 mm square permo power cable), there are 2 eaton fuse holder mounted inside the bottom trunking with 120 amp fuses fed from each string of batteries.   

Battery backup: 

2 strings - each made up of  4 x 105 amp/hr enertec premium heavy duty flooded lead acid batteries 

Now that i have done a little research and have a better understanding of inverters and battteries ( but still have a lot to learn), it is time to make a few modifications and upgrades.

The first thing I realised when I thought about doing maintenance on the system , no bypass switch, so that will be the first upgrade. Inverter/off/bypass switch will be installed.

The setup parameters will need to be checked and updated, I have already noticed that the setup has solar/utilty, there is no solar, so it will be corrected.

The batteries need to be checked:

Voltage tests at each battery terminal in each string.

A thermal scan of all the batteries, connections at the battery, the fuse holders and the inverter terminals.

The next thing is to look into installing a remote monitoring sytem to check the SOC and DOD, maybe using a Victron battery monitoring system. It might also be an idea to setup a a battery balancing unit ( still need to find out more about this and if it can be done using  lead acid batteries). I dont know how long these batteries are still going to last. Maybe another year or 2.

I have also considered removing 1 string at a time and using the hawkins charger to fully charge each battery individually, I dont know that that would help extend the life, and at the same time shuffle the batteries, for example put the inside 2 on the outside.

Any constructive input or advice would be appreciated. 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

 

IMG_6260.JPG

Edited by isetech

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...