Sunsynk Noob - Wiring question

Featured Replies

 

Good Day All

I have purchased a Sunsync inverter and am about to have it installed but I need to ensure that i have all the components on hand for when it's being installed. While this thread is quite detailed, I have been hearing mixed information about a relay and whether it is still required for a 5kva Sunsync inverter which has an ATS240.

1. Is the Sunsync inverters sold in 2023, still require the relay if it has an ATS240? Seems Growatt's has it built in.

2. Is there a way to wire the inverter so that the relay is not required?

3. Which relay exactly is required? Please provide a link

https://powerforum-store.co.za/collections/accessories/products/earth-neutral-bridge-box-for-ac-protection-box

  • Replies 53
  • Views 21.7k
  • Created
  • Last Reply

Top Posters In This Topic

Most Popular Posts

  • When the inverter is on island mode the neutral can float above earth potential. The relay connects the load out neutral to an earth spike to bring the neutral down to earth potential. You will need t

  • Step 1 -  Ensure "Islanding Mode" is selected on the Inverter Step 2 - Remove the BLACK NEUTRAL wire which is currently screwed into the NC (Normally Closed) terminal   Step 2 - C

  • branderplank
    branderplank

    1. Mine is wired to get power from Mains before RCD and from a "clean neutral". 2. Most guys just use a single NO/NC relay (240v coil). The coil will be connected to the live and neutral outputs

Posted Images

Hi Scorp

Thanks for the reply. This is a much cheaper solution. 

The link provided by Lee Page is for a 1 x N/C; 1 x N/O. However, you advised that it should be 2 N/C contacts.  Please confirm which is correct. Most suppliers seem to only have 2 N/O.

 

Hi Scorp

Thanks for the reply. This is a much cheaper solution. 

The link provided by Lee Page is for a 1 x N/C; 1 x N/O. However, you advised that it should be 2 N/C contacts.  Please confirm which is correct. Most suppliers seem to only have 2 N/O.

1 N/C will also work. While most relay will have 2 my idea was just to double up. 

You MUST have N/C as the coil gets power from the grid the N/E is broken. As soon as grid is gone the relay must make the N/E connection. 

Google 220V 10A relay and look at the one with base sold by Microrobotics. It has 2 change over contacts. 

You can buy the complete box too as posted earlier. It all depends on what combiner or protection box you are going to use. Many things are dependent of other equipment. 

Browse through customer installs and you will see some variations. 

So as tested with a multimeter, the Sunsync 5kw ats 240v switches off after 1 minute. This means that if a N/C ac contactor is used, it will bond when eskom power is present. 

I have heard from installers that they use N/O. 

Can someone please advise?

 

Edited by Tafseer007

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.