I have 2 King inverters connected in parallel and set to SUB.

But in the evenings when i lose PV and the batteries are fully charged, the master inverter still charge the battery at 10 A and the slave inverter uses 12 A battery power.

Is there some settings that I don't have right, or what should I do?

IMG-20210327-WA0002.jpg

IMG-20210327-WA0003.jpg

Link to comment
Share on other sites

1 hour ago, keyser511 said:

the master inverter still charge the battery at 10 A and the slave inverter uses 12 A battery power.

You need setting 16 to be one of the UdC options, either SbL/UdC or SLb/UdC. UdC means Utility Disabled from Charging.

I can't recall for sure, but I suspect that this is one of the settings that doesn't carry over from one unit to all the others, since you might want utility charging on one (for only 10 A charging for example) and not the others. I don't know if your monitoring software handles this, you may have to check/change settings from the removable display.