keyser511 Posted March 27, 2021 Share Posted March 27, 2021 Hello I have 2 King inverters connected in parallel and set to SUB. But in the evenings when i lose PV and the batteries are fully charged, the master inverter still charge the battery at 10 A and the slave inverter uses 12 A battery power. Is there some settings that I don't have right, or what should I do? Quote Link to comment Share on other sites More sharing options...
Coulomb Posted March 27, 2021 Share Posted March 27, 2021 1 hour ago, keyser511 said: the master inverter still charge the battery at 10 A and the slave inverter uses 12 A battery power. You need setting 16 to be one of the UdC options, either SbL/UdC or SLb/UdC. UdC means Utility Disabled from Charging. I can't recall for sure, but I suspect that this is one of the settings that doesn't carry over from one unit to all the others, since you might want utility charging on one (for only 10 A charging for example) and not the others. I don't know if your monitoring software handles this, you may have to check/change settings from the removable display. Quote Link to comment Share on other sites More sharing options...
keyser511 Posted March 29, 2021 Author Share Posted March 29, 2021 Thank you Coulomb, that solved my problem. Quote Link to comment Share on other sites More sharing options...