Help: New to solar with Kodak OG-Plus 5.48 inverter


Recommended Posts

Hi all, I’m new to the solar side of things and was previously using a Mecer Axpert 3Kva with 2x 200ah Oliter batteries. I had the opportunity to sell my current system and upgrade a bit. I’m on a very tight non-existent budget, but I want to do the right thing and will make a plan.

I’ve upgraded to the equipment listed below and had a solar installer install my PV panels. The 3x panels are connected in series. He did tell me right from the start that I don’t have enough PV panels. He then changed the setup with the settings that he suggested, but I found that the batteries didn’t charge and felt that the batteries were used too much. (Sorry I might still be in the battery as a backup mentality). I also noticed that my batteries % according to Watchpower v1.14 (RS232 - LAN cable) showed that they were on 47% at 51.90V with a 247W load. I’m worried because the % goes below 50%...

My average load during the day is about 250w - 600w max and my intention with the solar side was to hopefully be on solar during the day (saving a bit on Eskom) and then on utility during the evening.

Question 1: What would the suggested settings be with the equipment I have and way of use?
Question 2: Should I purchase 3 more panels and then how would they all be connected? Will it help or do I need even more?
Question 3: Is it ok to use the batteries and does this not significantly reduce the lifetime of the batteries?
Question 4: If a battery discharges a bit and then charges again is it then seen as a charge cycle?

I have raised these questions to the solar installer and he just said that his settings are correct and should stop worrying about what I see on the display panel and software.

Solar installers settings: 01: SBU, 02: 80A, 05: USE, 06: LTD , 07: TTD, 09: 50hz, 10: AUT, 11: 30A, 12: 49.0V, 13: 51.0V, 16: SLB/UCB, 18: BOF, 19: TEP, 20: LON, 22: AOF, 23: BYE, 25: FEN, 26: 57.2V, 27: 54.0V, 28: SIG, 29: 47.0V 

Any help or suggestions would be appreciated.


New Equipment:

Inverter - As per solar installers suggestion
Kodak King 5Kva Off Grid 48V
Model: OG-Plus 5.48

Specifications:
Rated Power                5000VA/5000W
Efficiency (Peak)            93% Line mode, 90% Battery mode
Solar Charger type            MPPT
Maximum PC Array Power        4000W
MPP Range @ Operating Voltage    60 VDC ~ 115 VDC
Max. PV Array Open Circuit Voltage    145 VDC
Max. Solar Charge Current        80A
Max. AC Charge Current        60A
Max. Charge Current            140A


Battery
4x Oliter 200ah Gel
Model: 12V200AH

Specifications:
Float charge                13.5V - 13.7V
Average charge            14.1V - 14.4V


PV Panels
3x AE Solar panels
Model: AE330HM6-60

Specifications:
Nominal Max. Power            Pmax (Wp)    330
Maximum power voltage        Vmp (V)    33.81
Maximum power current        Imp (A)    9.76
Open-circuit voltage            Voc (V)    41.31
Short-circuit current            Isc (A)        10.37
Module efficiency            (%)        19.90
Power tolerance            Pmax (Wp)    0 / + 5
Maximum system voltage DC        (V)        1000
Maximum series fuse rating        (A)        15

 

Link to comment
Share on other sites

5 hours ago, Anton P said:

I also noticed that my batteries % according to Watchpower v1.14 (RS232 - LAN cable) showed that they were on 47% at 51.90V with a 247W load. I’m worried because the % goes below 50%...

That's because your low battery cutoff is 47.0 V. The Axpert/Kodaks don't have a proper battery monitor, they just estimate the SOC with a crude formula that takes the cutoff voltage as -2% SOC, and adds 1% SOC for every 0.1 V that the battery voltage exceeds that setting. So (51.9 - 47.0) / 0.1 + -2% = 47%. The default cutoff voltage is 42 V, which works out better for SOC calculations (it would display 50% higher due to the 5.0 V lower cutoff voltage, so 97%!! The problem is, in South Africa you have the occasional load shed as I understand it, so running the battery down to 42 V (10.5 V per 12 V module) every load shed would ruin the battery very quickly. I would use a cutoff of 48 V (sometimes the highest possible value, though Kings will go to 54.0 V), which would make the reported SOC ever worse.

Usually I would recommend using an external battery monitor like a Victron BMV, but with your stated budget ("non-existent"), you should probably print out a cheat sheet from the internet, and place it beside your inverter, so you can do your own crude SOC estimation.

5 hours ago, Anton P said:

Question 1: What would the suggested settings be with the equipment I have and way of use?

Even though I have a King here for experimentation, I don't know them all that well. If you keep using little PV, you probably want to use a mode where the King will blend AC-in and solar.

As noted above, I would change setting 29 (low battery cut-off voltage) to 48.0 V. Setting 02 (maximum total charge current) seems very high at 80 A. Usually lead acid is limited to 0.15C, which for you is 0.15 x 200 = 30 A. I don't know your battery, it may be able to handle more than that, but I doubt it can cope with 0.4 C (80 A).

5 hours ago, Anton P said:

Question 2: Should I purchase 3 more panels

I don't know how you will pay for panels given your budget 🙂  But yes, 1000 W is low for a 5 kW system. Remember that you have more idle power now (the inverter chews more power doing nothing). You would benefit with 1, 2 or 3 more strings of 3 panels (3, 6, or 9 more panels).

Quote

and then how would they all be connected?

They must be very similar panels in terms of Vmp, preferably identical (but that's often hard to do). They should agree within 5%. Each string will need a separate string fuse (DC rated PV fuse of course). They should be wired 3S the same as your existing panels, unless by some amazing coincidence you can get 2S of monster panels to add up to within 5% of your existing 3S panels. All strings go to an isolating / combining / protecting box.

Quote

Will it help or do I need even more?

As above, it will help to feed the hungry 5 kW inverter's idle draw (even if you're only using a few hundred watts now). It will also help to offset Eskom usage. If you really only use 600 W of power, then more than one extra string is possibly wasted. But now that you have the ability to use it, I think you'll find more loads to put on the inverter.
 

Quote

Question 3: Is it ok to use the batteries and does this not significantly reduce the lifetime of the batteries?

Batteries are expensive. My view is that you may as well use them to save power bills. But in a high load shedding situation, it may make more sense to keep them as full as possible, so you have power for longer during the load sheds and blackouts.

Quote

Question 4: If a battery discharges a bit and then charges again is it then seen as a charge cycle?

It's not a whole cycle. So discharging 10% and recharging back to where it was is more or less 10% of a full cycle.

Link to comment
Share on other sites

14 minutes ago, Coulomb said:

That's because your low battery cutoff is 47.0 V. The Axpert/Kodaks don't have a proper battery monitor, they just estimate the SOC with a crude formula that takes the cutoff voltage as -2% SOC, and adds 1% SOC for every 0.1 V that the battery voltage exceeds that setting. So (51.9 - 47.0) / 0.1 + -2% = 47%. The default cutoff voltage is 42 V, which works out better for SOC calculations (it would display 50% higher due to the 5.0 V lower cutoff voltage, so 97%!! The problem is, in South Africa you have the occasional load shed as I understand it, so running the battery down to 42 V (10.5 V per 12 V module) every load shed would ruin the battery very quickly. I would use a cutoff of 48 V (sometimes the highest possible value, though Kings will go to 54.0 V), which would make the reported SOC ever worse.

Usually I would recommend using an external battery monitor like a Victron BMV, but with your stated budget ("non-existent"), you should probably print out a cheat sheet from the internet, and place it beside your inverter, so you can do your own crude SOC estimation.

Even though I have a King here for experimentation, I don't know them all that well. If you keep using little PV, you probably want to use a mode where the King will blend AC-in and solar.

As noted above, I would change setting 29 (low battery cut-off voltage) to 48.0 V. Setting 02 (maximum total charge current) seems very high at 80 A. Usually lead acid is limited to 0.15C, which for you is 0.15 x 200 = 30 A. I don't know your battery, it may be able to handle more than that, but I doubt it can cope with 0.4 C (80 A).

I don't know how you will pay for panels given your budget 🙂  But yes, 1000 W is low for a 5 kW system. Remember that you have more idle power now (the inverter chews more power doing nothing). You would benefit with 1, 2 or 3 more strings of 3 panels (3, 6, or 9 more panels).

They must be very similar panels in terms of Vmp, preferably identical (but that's often hard to do). They should agree within 5%. Each string will need a separate string fuse (DC rated PV fuse of course). They should be wired 3S the same as your existing panels, unless by some amazing coincidence you can get 2S of monster panels to add up to within 5% of your existing 3S panels. All strings go to an isolating / combining / protecting box.

As above, it will help to feed the hungry 5 kW inverter's idle draw (even if you're only using a few hundred watts now). It will also help to offset Eskom usage. If you really only use 600 W of power, then more than one extra string is possibly wasted. But now that you have the ability to use it, I think you'll find more loads to put on the inverter.
 

Batteries are expensive. My view is that you may as well use them to save power bills. But in a high load shedding situation, it may make more sense to keep them as full as possible, so you have power for longer during the load sheds and blackouts.

It's not a whole cycle. So discharging 10% and recharging back to where it was is more or less 10% of a full cycle.

Thank you for the response, so setup as is...change setting 2 to 30A and 29 to 48.0V. Any other suggestion as to setting changes?

Setting 2: Max charger current = (UTILITY + SOLAR) as per manual. I think that is why the installer set to 80A - default is 60A.

With the current settings will Utility charge the batteries and assist with load if solar not enough? We currently in winter so solar not very efficient and with the limited number of panels also not helping. I will be able to add an additional 3 panels at the end of the year and the combiner as suggested.

 

Link to comment
Share on other sites

On 2021/06/29 at 1:16 AM, Anton P said:

Any other suggestion as to setting changes?

See below.

On 2021/06/29 at 1:16 AM, Anton P said:

Setting 2: Max charger current = (UTILITY + SOLAR) as per manual. I think that is why the installer set to 80A - default is 60A.

200 Ah is pretty small (if lead acid) for a 5 kVA inverter. The worst lead acid batteries can only take 0.15C charge, which is 30 A. But perhaps yours can take more. Here is a picture I found on the web:

image.png.2b2f1eb19540bac71d814cf100c5b853.png

If similar to the above, you could change it to 50 A. Though with only 1000 W of solar, solar charging will only be 20 A until you get more panels. For faster utility charging, you could increase setting 11 (Maximum utility charging current) to be the same as setting 02.

Quote

With the current settings will Utility charge the batteries and assist with load if solar not enough?

At present, I think only if and when the battery voltage falls below that of setting 12 (back to grid). You might want to increase settings 12 and 13 (keep them at least 2 V apart) so the battery doesn't work so hard, and is more likely to be full at the end of an intermittently cloudy day.

Quote

We currently in winter so solar not very efficient and with the limited number of panels also not helping. 

In these conditions, you might want to switch setting 01 to SUB; that prioritises utility over battery for supplying the load. But I think when the sun is ample, you'd want to switch back to SBU, so the utility doesn't supply power every time a little cloud goes past. To do this switching comfortably, you'd want to have a monitoring program like Watchpower (free), so that you don't have to go out to the inverter every time you want to change this other settings. Or maybe just switch to SUB during winter, and back to SBU by spring; experiment to find what works for you.

 

Link to comment
Share on other sites

  • 6 months later...

I installed a Kodak OG-PLUS 5.48 Inverter
9x Canadian Solar Panels output 169 Volt
4x US2000 Plus Pylontech  batteries

Settings on inverter:-
02 - 30A                                                                    22 - AON                                              40 - Nrt  
05 - PYL which adjust 02, 26, 27 29 automatically 23 - bYE                                                93 - Nrt
06 - Ltd                                                                     25 - Fd5
07 - Ltd                                                                     26 - 56 V  (AUTO)
09 - 50Hz                                                                 27 - FLv     (AUTO)
10 - AUE                                                                    28 - SIG
11 - 30A                                                                    29 - AUTO CONTROLLED BY 05
12 - 46V                                                                    32 - AUE
13 - 54V                                                                    33 - Eds
16 - SbL                                                                    34 - EU (54V)
18 - bON                                                                  35 - 60 MIN
19 - tEP                                                                    36 - 30d
20 - LON                                                                  39 - Ad5

The inverter do not charge the batteries from the PV panels 169V input 
The inverter do not use PV for house usage but drain the batteries
My PC is connected via a RJ45 cable made up by computer tech

5. Code Reference:  received 61 alarm which is a communication loss between batt. and inverter

The above settings is more or less the same that i used on the Mecer 5kVa inverter which use Solar during the day and battery supply power during night  
Power consumption is 12 kWh / 24 period this include a 150 liter geyser with a 3kW element

 

Link to comment
Share on other sites

2 hours ago, Andries Taljaard said:

Kodak OG-PLUS 5.48 Inverter

So that's an Axpert King with orange paint. Unless it's an Axpert King II (these are still fairly new, I've never seen one), the absolute never-exceed PV voltage is 145 V. You're not supposed to exceed 115 V when actually operating, though in practice they'll probably work to 130 V, and start losing power from there.

So 169 V is probably stressing the components in the solar charge controller. I think that there are capacitors in there rated at 150 V.

I presume that your 9 panes are arranged 3S3P. They must be large panels, possibly with more than 72 cells, to have a Voc of 169/3 = 56.3 V. You'll have to arrange them as 2S4P, leaving one left over. You could use that to parallel your shadiest panel, putting the two panels most prone to shading in parallel. Or get one more panel the same as the others and make the array 2S5P, if that's not over 4800 W (i.e. 480 W panels or less).

2 hours ago, Andries Taljaard said:

Code Reference:  received 61 alarm which is a communication loss between batt. and inverter

You mentioned a cable between the PC and inverter; is there a special (not straight through) cable between the battery's BMS and the inverter? That's what warning 61 is about, and setting 05 = PYL requires this cable.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...