Hi all,

 

Recently installed Sunsynk (5 weeks running OK and impressed with the machine). It threw out the following codes this morning - have checked forums and manuals - wondering if anyone has seen them before. I suspect bad grid power has something to do it - will see how it runs tonight again.

Sunsynk 5Kw

2 x Pylontech US3000C

10 x JA 455s

(Used in area with Prepaid meter)

 

Hoping someone can help with:

1. Anyone seen any of the codes before? Particularly F03. Also why F13 is continuously coming up every 2/3mins before the DC Low came up. It might be linked to this - but what would prevent the inverter from switching to grid when the batteries reach the specified time of use SOC - e.g. 35% below? Bad grid being filtered by the inverter settings?

2. CT coil - have watched the videos - I have the old software. The software has a “HM” signal to show wattage and this is reflecting a negative wattage - which I take to mean they installed it the wrong way? I know it clearly says CT on the new software - just confirming my assumption that this used to be “HM” on the old screens? I’m set to Zero export>Load only so hopefully no impact. Will correct the CT coil and switch to HM load too.

3. When exporting once battery is full to non essentials - this is ONLY excess solar right? I.e. non essentials will not use battery.

4. My time of use functions are included below. I’ll tweak them a bit for loadshedding - however - what would happen if I changed the 35% to say - 50% in all lines that have 35%. And the Grid went off. Would the time of use settings mean that I couldn’t use my power if my batteries were down to 50%? Or does time of use get overridden when grid is shut down.

 

Thanks - apologies if these have been asked elsewhere. Has anyone received the beta of the new data logger? Interested to know thoughts.

 

Cheers and thanks in advance.

 

Time of use:

B2E54F51-006B-4143-8839-77F1A6299D50.jpeg

 

Fault codes - note grid was down when pic was taken. I suspect bad grid caused this but not sure why the inverter didn’t switch to the grid when the batteries hit 35%.

425A9CB4-682A-472F-9476-131A6D76119A.jpeg

Edited by MINUS
Link to comment
Share on other sites

  • MINUS changed the title to Sunsynk 5kW fault codes + general UI questions

If you have old software, then as a start, I'd recommend updating it.

On your error codes, I have never seen them before, F56 is a battery related error, check cables, connections, battery discharge settings and condition of battery. F13 seems informational, suggests that someone was changing grid mode / work mode parameters. And as for F03, I don't know what GFDI stands for.

If your CT coil is installed incorrectly then the CT value in the info screen will be negative:

image.thumb.png.0d3c3a7ccb42a5a423e7a5fd3160b4f7.png

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...