Prepaid Meter "Tripping" for a few seconds


JeremyJvR
 Share

Question

Good day all,

I have a newly installed Deye Hybrid Inverter. (Which I am led to believe is the same as Sunsynk and Fusion)

The system is connected to the grid with a CT, the CT is currently pointing towards the inverter. When I point it towards the Grid, the inverter gets negative values towards the grid (Which I believe means it is "selling" to the grid). The inverter however is set on "zero export to CT"

Currently I have 2 issues:

1. The prepaid meter trips momentarily every now and again, it happens mostly around 1 pm and 4 pm. It will trip for about 20 seconds then come back up, it will do this 3 to 4 times in a row. I cannot point to a specific scenario where it trips, ie. High load, Low load, No load. It happens completely random.

2. Because it is a Bi-Directional inverter (Or so I believe) I have my High Load items connected to the "Grid" side of the inverter and my Low load stuff to "Load". When the Grid drops due to the trip in the prepaid meter, my high load items trip with it. Shouldn't these items stay on? At that point in time there are more than enough power coming from the panels and should be able to keep my loads running?

I am attaching a rough diagram of how it is currently connected. The Grid and "Load" neutrals are split and running separately. Earths are all connected together.

Hoping someone out there can give me some answers.

Thanks

Jeremy

Capture2.PNG

Link to comment
Share on other sites

6 answers to this question

Recommended Posts

  • 0
24 minutes ago, abeetude said:

The way I understand it, your CT is in the wrong place. See the revised diagram below

 

Capture2.thumb.PNG.3803dad952a57a14fa83a50ef9498bc3.png.c76e683257cff83506c39f4a81f3d541.png

So it turns out that the Conlog meters have some sort of programming to be done to disable a safety feature within it to allow "leakage" from the inverter that almost contently pushes about 20w of power through the meter.

The second issue of the CT is that the when using a Deye inverter, the arrow on the CT should point to the DB and not to the grid as showed by the manual.

So it seems like my issue has been resolved.

Link to comment
Share on other sites

  • 0
5 hours ago, JeremyJvR said:

So it seems like my issue has been resolved.

Hi @JeremyJvR glad you got it sorted!

All makes sense in your reply except the position of your CT coil as per your original drawing cant be correct. The way your drawing indicates - feedback will occur. The CT coil help prevent current flowing back into the meter therefore it needs to be before the meter and not in between Eskom and the Meter.

Link to comment
Share on other sites

  • 0
46 minutes ago, abeetude said:

Hi @JeremyJvR glad you got it sorted!

All makes sense in your reply except the position of your CT coil as per your original drawing cant be correct. The way your drawing indicates - feedback will occur. The CT coil help prevent current flowing back into the meter therefore it needs to be before the meter and not in between Eskom and the Meter.

Yeah, I switched the position to after the meter. Punched in some coding, and this far no trips yet. Hopefully it's sorted now. Now I can get the COC done. Thanks for your replies, I really appreciate it

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Answer this question...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...