Johan Grobler reacted to zsde in RCT Axpert 5K Solar helpThose panels have a VOC of 49,4V let's work on 50V. That means you can only put 2 of those in series as on a cold day 3 would exceed the 145V max VOC.
With 2 in Series you'll be safe and satisfy the 60-114VDC range
Operating current is 13,14 Amps.
With two in series you would have a theoretical 1090W which will probably never happen in real life.
So my thoughts are 3 strings of 2 series panels each in parallel will probably provide you with the optimal set up with this inverter.
-
Johan Grobler got a reaction from zsde in RCT Axpert 5K Solar helpThank you very much, this helps a lot. I now just need to find brackets and isolators for the panels👍👍