Cable size
Eish ok. So if it runs on 1 pump and doesn't trip, can I just run a 2nd 4mm instead of running a 10 or 12? Also, we have it so the main DB is feeding a sub DB, then from the sub it runs to the pump station. We fed the sub DB from the main house with a 4mm as well - obviously that would also need to be upsized?
-
Cable size
Thank you. This is what I thought and proceeded to do. The client sent me the following message after the irrigation guys installed the pumps. Sidenote, the distance is actually only 60m. "Hi Ty. Sorry for the bad news but the cable is too thin. The voltage drop is too great over the distance and causes a low voltage trip at the pump station. Looks like we’ll have to go to a 10mm cable. The irrigation contractor mentioned that a 10mm SWA cable is normally used"
-
Cable size
Hi there, Can 2 x 2.2kw 15A water pumps run on a 4mm cable with around 100m distance?
- 12Kw Deye
-
12Kw Deye
Ok great! thank you very very much!
-
12Kw Deye
Hi there, Yes sorry, I want to put 1 string if 10 panels on mppt 1 and another string of 10 panels on mppt 2. This will be ok?
-
12Kw Deye
Hi All, I have a client who has an existing 12kw Deye inverter and she wants to add panel. The roof is limited with space. Am I able to put 10 x 550w panels on string 1 and another 10 on string 2?
-