Jason Varney reacted to Chris Hobson in 2.9kw from 2.4kw pvs?What you need to remember that the Axpert reports PV Amps after the MPPT so those amps are flowing internally within the SCC. It is easy to see that this is the case. Multiply PV Amps by PV Volts and you will get a Watt value much higher than the PV production at that point in time. Multiply it by battery voltage and you get a value within 50W of the reading the Axpert shows.
https://powerforum.co.za/topic/222-karoo-farm-installation/?do=findComment&comment=1552