September 20, 20223 yr Hi all, Excuse my ignorance, I Have a Growatt inverter and NEnergy battery. The inverter does recognise the battery as Lithium and defaults to AGM. Is it a problem if I leave it as AGM and not Lithium? My next step is to the get supplier to change the battery to a Shoto or Pylontech. Appreciate your feedback. Thanks
September 23, 20223 yr What BMS comms does the battery have ? If you selecting Li on Menu 005, you have to select the correct protocol . if there is no BMS comms, I would recommend option USE on 005 instead of AGM. then you have to define menu 019, 020, 021 as per battery specs.
September 23, 20223 yr Author 3 hours ago, Mzala said: What BMS comms does the battery have ? If you selecting Li on Menu 005, you have to select the correct protocol . if there is no BMS comms, I would recommend option USE on 005 instead of AGM. then you have to define menu 019, 020, 021 as per battery specs. Thank you, I will check
September 30, 20223 yr The Growatt manual recommend USE 2 for lithium voltage based setup, equalization needs to be disabled.. The lithium protocol for Pylontech is L52 for the CAN connection, you also need a 120 Ohm terminator on the unused CAN connector on the battery.